Discuss Dual Tariff Supply where do you take the Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
39
Where do take the Ze on a dual tariff supply? At the 4 pole isolator (or do you change it to a circuit breaker)at the service head or in the consumer unit?If at the consumer unit which supply, the supply from isolator to consumer unit is a 16mm t&e. Your help will be greatly appreciated.
 
Technically, you have two installations.
So you can either measure Ze at each board, or if there is a single 4 pole isolator for both boards, you can measure there.
The supplies are in one board and they are fed from the 4 pole isolator. Why I am asking for advice is the 16mm T&E has a 6mm cpc which is obviously not 16mm.
 
Left hand meter feeds the top Time switch.
The left hand 4 pole isolator isolates the off peak feed from the time clock, and the normal rate feed from the meter.
Then there’s two T&Es from the 4 pole isolator going into the building.
Right hand meter feeds the bottom Time clock and the right hand 4 pole isolator.
 

Reply to Dual Tariff Supply where do you take the Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Until last week I had a dual tariff electricity supply with a cheaper overnight tariff. This was good for the storage heating, but now the storage...
Replies
2
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
799
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
Replies
1
Views
678
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock