Thanks for the replies chaps, that was a close en Wiko. My son's having an extension done. When they were digging the footings, they found some unexpected drainage pipes. Thames Water came out and camera'd them, and found another waste pipe. Both were 3' feet down, and if I'd look for a place to put a rod, I'd hit both!

If this 18th proposal goes ahead, it might prove expensive.

With all little bit of planning it should be possible to arrange to use the reinforcing in the concrete as the earth electrode on new builds and extensions.
 
With all little bit of planning it should be possible to arrange to use the reinforcing in the concrete as the earth electrode on new builds and extensions.

I understand that's the provision. However, if the requirement for earth rod is applied to 132.16, and I'm putting an extra socket in an old terraced house in the town centre, it's going to be difficult and not cheap.
 
If I stand corrected I thought the draft said on the lines of preferably. I think that they will accept that when you go around to Mrs Muggins house to fit an extra socket it would not be practical to go and run earth cable outside to a earth electrode.
 
If I stand corrected I thought the draft said on the lines of preferably. I think that they will accept that when you go around to Mrs Muggins house to fit an extra socket it would not be practical to go and run earth cable outside to a earth electrode.

Reg 542.1.201 .........Additionally, there shall be an earth electrode, supplementing any earthing facility provided by the distributor, in accordance with 542.2.3 (which describes earth foundations).

Still not quite clear on this draft reg, perhaps I (and others have read it incorrectly?)
 
Back to my post.
Should of mention the service head is 2 separate connection blocks

And there is no earth coming off the neutral.

2 cables come in from the roof stright to the service connections
 
I'm confused having just read this thread....first it was a possible TNS with a strap on the sheath....now it's two singles coming in overhead?
Am I missing something?
 
Will have to get one when I go back.

IMG_20170811_201826_412.jpg
 
bigger pic would help.showing where all them cables go to/come from.
 
The lower SWA is an outgoing circuit......the incoming supply is top left of the pic and is not completely shown. There appears to be a braid connected to the MET, where does that go?
 

Reply to Earth arrangements confusion in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
3K
Been asked to do some rewiring, and have said needs upgrade of consumer unit really Main question is regarding earthing - Zs reads at 0.45 ohms...
Replies
7
Views
1K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
Replies
30
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock