Discuss Earth Bonding - LPG Pipe That Does Not Go Underground in the DIY Electrical Advice area at ElectriciansForums.net

aesmith

-
DIY
Reaction score
25
Hi,
Our cooker is LPG, fitted on the inside of an outside wall if that makes sense. The gas pipe runs internally then through the wall to the regulator and changeover unit mounted outside, around 4' off the ground. The pipe doesn't go underground at any point.

My understanding is that it doesn't need bonding, the original gas fitter clearly agree as he marked it as "N/A" on the Gas Safety Certificate. However the guy that just did a service wasn't quite happy, he expected to see earth bonding and was a bit dubious.

So my questions are (1) am I correct that bonding isn't needed? And (2) assuming it's not needed, is there any issue with adding it anyway, just to keep any future gas fitter happy?

Thanks, Tony S
 
So to be clear, this is a propane tank fed arrangement?
 
Sorry, the gas supply is two 19kg cylinders each connected by flexible hose to the changeover switch.
 
OK, so you're quite correct in thinking that this doesn't need bonding (BS7671 411.3.1.2 refers.....) However, whether you want to attempt to have that conversation time after time with the less informed or just pay to get it done regardless is entirely up to you!!
 
However, whether you want to attempt to have that conversation time after time with the less informed or just pay to get it done regardless is entirely up to you!!
That was exactly what I was thinking. For example the current certificate notes "Could not see evidence of earth bonding. Instruct an electrician to check gas pipe and add bonding if none present."

I take it from your response that there's no actual disadvantage or safety concern about installing bonding in this case, even if not actually needed?

Strictly we don't actually need to do anything as there's no requirement for a current certificate anyway. But I'd prefer that the installation is such that it would pass if the requirement ever came about.
 
  • Like
Reactions: DPG
I posted the same question last week, although my gas pipe was feeding a boiler, and was connected to the water pipework internally at the boiler.

Whatever the regs say, I would be inclined to make sure it’s earthed… just in case some fluke instance happens and your hob becomes live..(electric ignition?) then you would have a live hob, and live gas pipes…

All it would take would be a small spark….
 
I posted the same question last week, although my gas pipe was feeding a boiler, and was connected to the water pipework internally at the boiler.

Whatever the regs say, I would be inclined to make sure it’s earthed… just in case some fluke instance happens and your hob becomes live..(electric ignition?) then you would have a live hob, and live gas pipes…

All it would take would be a small spark….
There's actually a counter-argument that by bonding when not actually necessary that we add the potential for an earth fault path to exist where none existed before, so these things do need skilled judgment.
 
There's actually a counter-argument that by bonding when not actually necessary that we add the potential for an earth fault path to exist where none existed before, so these things do need skilled judgment.
Totally agree.
That's why the OP is asking for our skilled judgement rather than taking the word of a gas engineer.

Not sure of the OP's situation, but certainly my own, there is a parallel path to Earth through the other copper pipes and the flex from the spur to the boiler.
 
That was exactly what I was thinking. For example the current certificate notes "Could not see evidence of earth bonding. Instruct an electrician to check gas pipe and add bonding if none present."
Sounds like the gas engineer has already decided the outcome!!!!
 
Thanks for all the comments. I don't strictly need a gas safety certificate for our own house, but if the need arises I could use a different gas fitter. This guy also wanted to see a CO alarm, even though the actual guidance says ..
CO detectors to be fitted in all rooms where there is a fixed combustion appliance (excluding an appliance used solely for cooking) or a flue.

However I've not been able to put my finger on the actual legislation governing that requirement. My quote comes from the "Tolerable Standard Guidance
Tolerable Standards
 

Reply to Earth Bonding - LPG Pipe That Does Not Go Underground in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Disclaimer: I'm not going to attempt this job myself, I want a professional to do this job properly since I consider it non-trivial and need it...
Replies
2
Views
970
Hi guys I am working in a warehouse where there is an inactive gas pipe and disconnected gas meter. The DB which has been upgraded now is on the...
Replies
6
Views
1K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
207
A 'Sunday challenge' for the qualified electricians.... Can anyone explain why a built-in gas meter housing box that is located 600mm above a...
Replies
8
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock