Hi all,
My first post-don't be too hard on me!
I'm bonding an existing 3-phase power supply (150mm2 SWA cable) to various incoming services: Sprinkler main, water, compressed air, gas steam & condensate etc. According to BS7671, I can run 35mm2 wire. The run to first service from main earth terminal is about 25m but once there, services are max. 2m apart.
Is it allowed to crimp 2 x 35 wires into say a 70mm crimp ring connector to jump from service to service? Although the conductor is cut, it is permanently joined together. Could even run solder into crimp terminal.
The other issue I have is connecting such a large lug to 15mm copper pipe clamp(s). There is no mention in regs. about possibility of an auxiliary earth terminal, then radiating out from such a terminal separately to each service. This would save so much wire.
Regards
Dave
 
I would use 2 x 35mm lugs. the cable does not need to be unbroken. just continuous. which it will be once the 2 lugs are bolted together.
 
I'd crimp a 35mmsq cable into an tubular terminal that's designed for 35mmsq cable... then bolt together as Tel says or bolt to a busbar etc. Shovin' 2x35mmsq into a terminal that's designed for 70mmsq cable is not a good idea. There are terminals designed for 2 cables, but again they are designed for the task and will require special crimp die sets.

Also, a properly crimped terminal shouldn't have any room for any solder to flow into it. If there is, it's not properly crimped.

...MHO of course.
 
Hi all,
My first post-don't be too hard on me!
I'm bonding an existing 3-phase power supply (150mm2 SWA cable) to various incoming services: Sprinkler main, water, compressed air, gas steam & condensate etc. According to BS7671, I can run 35mm2 wire. The run to first service from main earth terminal is about 25m but once there, services are max. 2m apart.
Is it allowed to crimp 2 x 35 wires into say a 70mm crimp ring connector to jump from service to service? Although the conductor is cut, it is permanently joined together. Could even run solder into crimp terminal.
The other issue I have is connecting such a large lug to 15mm copper pipe clamp(s). There is no mention in regs. about possibility of an auxiliary earth terminal, then radiating out from such a terminal separately to each service. This would save so much wire.
Regards
Dave
Fit a local Earth bar and bond all your services to this bar, make sure the Bar is labeled as a bond connection.
 

Reply to Earth Bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
298
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
574
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
710
This is my first post and I hope I explain it correctly/ Simply. 1100sq foot single family home, 100 amp service. I am having an electrician...
Replies
2
Views
904

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock