How to test an earth electrode resistance for Lightning Protection System in the middle of large concrete pad? I cannot not find a soft ground for spikes to drive in for testing. Is there any other ways of measuring the earth electrode resistance value?

Thanks

Laxi
 
Last edited by a moderator:
Have a look at hiring (or purchase at £500+) an earth resistance clamp which induces a current into the system without you needing to disconnect the main earth.

Or, as above an impedance test
 
Have a look at hiring (or purchase at £500+) an earth resistance clamp which induces a current into the system without you needing to disconnect the main earth.

Or, as above an impedance test

The trouble with those earth clamps, is that you need room to get the jaws around the earth rod, and there is generally very little room to do this when earth rods are within a flush to ground earth pit...

EDIT... How many electrodes (earth rods) are there along each side of the building being tested and how far apart are they?
 
Last edited by a moderator:
The trouble with those earth clamps, is that you need room to get the jaws around the earth rod, and there is generally very little room to do this when earth rods are within a flush to ground earth pit...

EDIT... How many electrodes (earth rods) are there along each side of the building being tested and how far apart are they?

Hi,
Thanks for your help on this matter. I am actually testing earth rod resistance for Lightning Protection System. There are four down conductors on each corner of the building. I managed to measure all three earth rod resistance value. But there is no soft ground around the electrode rod that belongs to fourth down conductor. One 2 m long copper solid rod is being used on this down conductor . The nearest soft ground is approximately 40m away from the test point. The surrounding area is concrete pad.

Is there any means of testing the earth electrode resistance for Lightning Protection System?

Thanks

Laxi
 
Unless this building is very small say 10m to 15m square, then it doesn't sound like you have enough down conductors depending on what the building is and building construction material.

You could use weighted metal plates in contact with ''wet'' concrete in place of your test spikes and compare values with that of the other 3 earth rods. BTW i've more often than not used test leads in excess of a 100m for the C1 test spike. So 40m isn't, as far as i'm concerned any great distance when testing earth rods...
 
Hi,
Thanks for your help on this matter. I am actually testing earth rod resistance for Lightning Protection System. There are four down conductors on each corner of the building. I managed to measure all three earth rod resistance value. But there is no soft ground around the electrode rod that belongs to fourth down conductor. One 2 m long copper solid rod is being used on this down conductor . The nearest soft ground is approximately 40m away from the test point. The surrounding area is concrete pad.

Is there any means of testing the earth electrode resistance for Lightning Protection System?

Thanks

Laxi
if you are using Megger equipment to do your testing there is no need to sink the spikes if you can't. Speak to Megger technical and they will walk you through the test procedure.
 

Reply to Earth Electrode Testing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area...
Replies
1
Views
421
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
1K
Hi. The question is..... can saturated ground affect earth resistivity testing equipment? Some days there's an unacceptable earth reading, another...
Replies
8
Views
359
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
590
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
759

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock