treak

Does anyone have any experience in recording values of EFLI on circuits fed through a DB supplied via a UPS please? The meter shows the above scale arrow.
I understand that there will be no reference to the external earth due to the inverter inside the UPS but what will happen to the UPS supplied circuits under fault conditions in normal supply mode? Is this something to be taken up with the manufacturer? Then there is next question how does the UPS deal with a fault in power failure mode? Not to worried about the second part, I obviously need to take some readings of EFLI to record and to see if they are sufficent to meet disonnection times.
Any help would be great.
 
You are only measuring the impedance of the output stage of the UPS.

Record values on bypass and remember that the UPS itself will clear any faults by limiting it's own short circuit current and eventually shutting down-often at around 100mS to protect the inverter and any damage downstream caused by the fault.
 

Reply to Earth fault loop impedance readings through a UPS supply in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
527
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi Just bought this 1960s house, will be doing full rewire. Incoming supply splits and goes through hole in garage to next door. This is a looped...
Replies
25
Views
5K
Hi everyone, I have a particular job visited this morning, that on all circuits, at each point, i got a reading off around 25ohms for a earth...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock