Discuss Earth fault loop impedance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

:) thanks

so working with the tabulated values I'm given in my material would the formula I posted be the right way to go about it?

I am of the opinion that the course material is out of date as the Cmin factor of 0.95 is already worked into the new maximum values.
The question is simply asking for you to apply the temperature correction factor to the maximum values and compare those values with the given measured values and state whether compliant or not.

You could point out in your answer that the Cmin factor of 0.95 should be applied if you would like to illustrate you have been given out of date material.
 
I am of the opinion that the course material is out of date as the Cmin factor of 0.95 is already worked into the new maximum values.
The question is simply asking for you to apply the temperature correction factor to the maximum values and compare those values with the given measured values and state whether compliant or not.

You could point out in your answer that the Cmin factor of 0.95 should be applied if you would like to illustrate you have been given out of date material.

Yes I would like to do that :)

seems negative learning material that is out of date
 

Reply to Earth fault loop impedance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
591
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
751
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
2K
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K
Can someone explain this to me? The regs book calls Zs 'Earth Fault Loop Impedence' and the On-Site Guide calls Ze 'Earth Fault Loop Impedence'.
Replies
6
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock