Cable operating temperatures and limiting temperatures under fault conditions are two entirely different scenarios...
Yes you're right....I'm easily confused these days!
Discuss Earth Faulth Loop Impedance HELP!!! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Cable operating temperatures and limiting temperatures under fault conditions are two entirely different scenarios...
The 80% rule of thumb is only intended to be applied to a test result taken from an impedance test. You have to ensure that the tested value does not exceed 80% of the tabulated value.
If the value is above 80% of the figure then improve the result this can be done by improving or providing additional earthing.
Reply to Earth Faulth Loop Impedance HELP!!! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net