Currently reading:
earth leakage

Discuss earth leakage in the UK Electrical Forum area at ElectriciansForums.net

ipf

-
Mentor
Esteemed
Arms
Reaction score
6,972
Called out by an old couple this aft, power down at a bungalow. Hour to spare so arrived to find main switch 30mA rcd tripped. Handy man/son had made the loft hatch bigger for new step ladder system. Bunch of cables must have been at the side of the hatch....butchered and extended with all sorts and colours of cables and different sizes of connectors, what a mess. Sorted anyway.
Tn-s, Zs 0.36. Various other problems, no bonding to gas or water included
Loads up ready for off, short of time and late. She then puts the dryer in the extension on....trip. Had a look, a bit of a mess, more like a timber shed..2 ds's each with d adaptors...washer, dryer, f/freezer...

Anyway, did an earth leakage test on the MEC...0.5 amps
Why is the RCD not tripping anyway. Tested at a local socket on 30mA, no problem.
 
Take it your saying tripped when tested at socket. = ask a real spark not me

- - - Updated - - -

Dodgy clamp meter,

- - - Updated - - -

Test each cpc separately , to see if specific
 
Anyway, did an earth leakage test on the MEC...0.5 amps
Why is the RCD not tripping anyway.

For a true leakage reading you need to clamp the supply tails, L & N together. If there are extraneous parts bonded to the MET or connected via a CPC, any current measured in the earthing conductor won't necessarily reflect the true leakage current.
 
For a true leakage reading you need to clamp the supply tails, L & N together. If there are extraneous parts bonded to the MET or connected via a CPC, any current measured in the earthing conductor won't necessarily reflect the true leakage current.

Appreciate that, mate, problems and no time though.Quick test, there's only the MEC connected , but who knows throughout the place.
 

Reply to earth leakage in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock