- Reaction score
- 6,963
Called out by an old couple this aft, power down at a bungalow. Hour to spare so arrived to find main switch 30mA rcd tripped. Handy man/son had made the loft hatch bigger for new step ladder system. Bunch of cables must have been at the side of the hatch....butchered and extended with all sorts and colours of cables and different sizes of connectors, what a mess. Sorted anyway.
Tn-s, Zs 0.36. Various other problems, no bonding to gas or water included
Loads up ready for off, short of time and late. She then puts the dryer in the extension on....trip. Had a look, a bit of a mess, more like a timber shed..2 ds's each with d adaptors...washer, dryer, f/freezer...
Anyway, did an earth leakage test on the MEC...0.5 amps
Why is the RCD not tripping anyway. Tested at a local socket on 30mA, no problem.
Tn-s, Zs 0.36. Various other problems, no bonding to gas or water included
Loads up ready for off, short of time and late. She then puts the dryer in the extension on....trip. Had a look, a bit of a mess, more like a timber shed..2 ds's each with d adaptors...washer, dryer, f/freezer...
Anyway, did an earth leakage test on the MEC...0.5 amps
Why is the RCD not tripping anyway. Tested at a local socket on 30mA, no problem.