Hello I’m a student learning about industrial wiring and circuits and we’re about to start learning about how to do loop impedance calculations. I have made a drawing of a three phase installation and was wondering if anyone could give me information on how I get the Ze Zs and R1 + R2. How would I do this with a three wire loop impedance meter and also how would I do it without one. Any help is appreciated, just trying to get my head round it first before we start the lessons. Photo is attached.
 

Attachments

  • D7714230-606E-4F61-A859-D85420B548C8.jpeg
    267.8 KB · Views: 27
Ze at the live side of the main isolator with earth disconnected, so isolator OFF. now you have a go at how to get R1+R2 and we cannthen see if you have ther right approach.
 
Ze at the live side of the main isolator with earth disconnected, so isolator OFF. now you have a go at how to get R1+R2 and we cannthen see if you have ther right approach.
0.5ohm with earth disconnected and testing the earth back to the supply with the loop impedance meter. How do I get R1 and r2 and can you get it without a meter. Thanks
 
R1 is the phase conductor. R2 is the cpc. add them and get R1+R2, or short 1 end and measure in 1 hit. you need a meter set on continuity (low ohms). measure each phase-E. all 3 should be the same reading.
 
r1 and r2 (lower case) denotes end-end for a ring. important that you distinguish. you measure from isolator to control panel then from panel to motor and add them together.
 
,multimtercon ohmscand MFT on ohms should give same readings for R1 and R2 etc.. a multimeter can't measure Zs which is a live test.
 
,multimtercon ohmscand MFT on ohms should give same readings for R1 and R2 etc.. a multimeter can't measure Zs which is a live test.
I think I understand now. I’ve attached my notes. I then add my r1 R2 reading to my Ze reading to get my zs? Does this all look correct ? Thanks
 

Attachments

  • 5B68CFC3-1CA4-4C41-8E23-793CE3E521A8.jpeg
    284.7 KB · Views: 11
I think I understand now. I’ve attached my notes. I then add my r1 R2 reading to my Ze reading to get my zs? Does this all look correct ? Thanks
yes but please get into the habit or R1 as opposed to r1. etc. 2 entirely different measurements. in an exam you'd be marked down otherwise.
 

Reply to Earth loop fault impedance help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
581
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
750
Confused as to what the earth fault loop is. I'm aware it's the path that fault current takes (Line-Earth) but how many times does fault current...
Replies
7
Views
1K
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
2K
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock