Hai all,
What will happen if I didn't remove the earth cable from earth pit while taking earth Resistance.
Is that mandatary to remove the earth cable from pit while taking resistance using earth tester
 
You do not need to remove the earthing conductor from the earth electrode specifically but the earthing rod must be disconnected from the electrical installation, so it is possible to just disconnect the earthing conductor from the main earth terminal (with the installation powered off).
If the earth electrode remains connected to the installation then any extraneous parts will act as additional earth rods and invalidate the test results for the electrode you are testing.
 
Hi - if the means of earthing (the earth rod, tape or what ever) is not isolated then you will be measuring other things in parallel with it. So you may get an incorrectly low reading, would be my thought.
Edit - RB has it :)
 
You would get a false reading and maybe assume it meets requirements when it does not. I know that has been covered above but not stated explicitly.
 

Reply to Earth Resistance checking without removing earth cable from earth pit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area...
Replies
1
Views
410
Hi, I've bought a "yagusmart" smart switch from Amazon and it has no earth terminal. Although there are no metal facing parts I would think the...
Replies
2
Views
567
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
523
I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...
Replies
44
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock