Posting a message to the forum will remove the above advertisement

  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.
  2. Electrical 2 Go - Electrical Supplier and Electrical Wholesalers

    Please visit our prime electrical forum sponsor - they have the best tools at the best prices. If you find a price better somewhere else, call them or contact them, and they may be able to beat it for you. Especially on an order of a few items.

    Dismiss Notice

Discuss Earth rod needed for shed supply or pme allowed ???? in the Electrical Forum area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Tim collins
    Offline

    Tim collins EF Member

    Location:
    London
    should you install a earth rod if running a feed to a shed which is built on timber frame and is all timber , no metal parts and will have no services ie gas or water in it so no need for bonding only a supply for a light and a couple of sockets or can you use a pme earth from fuseboard if the shed supply is run in 6mm armoured from the outside of the house ( inside house 6mm t+e to fuseboard ) protected by 32amp rcbo will be installing a 2 way board with rcd main switch in shed approx 25 meters away
     
  2. Des 56
    Offline

    Des 56 Forum Mentor

    Location:
    Gliese 581C
    Rod not necessary
    Whats the score with the 2 Rcds?
     
    • Agree Agree x 3
  3. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    Why not swa from board to board
     
    • Agree Agree x 2
    • Like Like x 1
  4. TJ Anderson
    Offline

    TJ Anderson Forum Mentor

    Location:
    Derby
    More fun at testing time? "Which is gonna trip" lol
     
    • Like Like x 1
    • Funny Funny x 1
  5. Strima
    Offline

    Strima Electrician's Arms

    Location:
    St Neots
    What’s the earthing arrangement at source?

    Have you spoken to your CPS tech helpline?
     
    • Optimistic Optimistic x 1
  6. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    How is the 6.0mm T & E run?
     
    • Like Like x 1
    • Optimistic Optimistic x 1
  7. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    Why are we assuming the OP is in CPS scheme?
     
    • Like Like x 1
  8. Strima
    Offline

    Strima Electrician's Arms

    Location:
    St Neots
    I’ve got nothing better to do tonight.
     
    • Funny Funny x 3
  9. TJ Anderson
    Offline

    TJ Anderson Forum Mentor

    Location:
    Derby
    That helpline is technically only to help them obtain payment from a bank account!
     
    • Like Like x 2
    • Old Old x 1
  10. Tim collins
    Offline

    Tim collins EF Member

    Location:
    London
    From fuseboard clipped in ceiling void then into cupboard and in trunking before drilling hole outside and terminating to armoured in a wiska box ( client doesn’t want any chasing )
     
    • Creative Creative x 1
  11. Tim collins
    Offline

    Tim collins EF Member

    Location:
    London
    The earthing arrangement is pme , in process of joining cps scheme tried ringing for advice and they said they can’t give me any advice as not member yet
     
  12. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    What scheme is that? Whenever I rung Elecsa tech helpline, they never asked me anything to verify membership.
     
    • Agree Agree x 1
  13. essex
    Offline

    essex Forum Mentor

    Location:
    Wiltshire
    You almost got a 'dumb' from me then.
     
    • Funny Funny x 1
  14. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    Well done for responding ..... So many don't or simply get stroppy
     
    • Like Like x 3
  15. Flanders
    Offline

    Flanders Regular EF Member

    Location:
    Tamworth
    As Mudroch and Des mentioned don't install two30ma Rcds in line with each other and why use T&E how are you running it outside ?, I Would use Swa and so there will be no nead for a rcd at the supply end
     
    • Like Like x 1
Loading...
Similar Threads - Earth needed shed Forum Date
electrician needed for earth testing Looking for Domestic Electricians? May 10, 2019
Advice needed on unconnected earth wire. Electrical Forum Apr 28, 2019

Share This Page

Users found this page by searching for:

  1. shed on pme with rod

    ,
  2. earth rod cable size for outbuilding

    ,
  3. pme supply for separate garages

    ,
  4. pme earth,
  5. pme supply
Electricians Directory Post a Domestic Job Post a Commercial Job