  1. Tim collins
    Offline

    Tim collins EF Member

    Location:
    London
    should you install a earth rod if running a feed to a shed which is built on timber frame and is all timber , no metal parts and will have no services ie gas or water in it so no need for bonding only a supply for a light and a couple of sockets or can you use a pme earth from fuseboard if the shed supply is run in 6mm armoured from the outside of the house ( inside house 6mm t+e to fuseboard ) protected by 32amp rcbo will be installing a 2 way board with rcd main switch in shed approx 25 meters away
     
  2. Des 56
    Offline

    Des 56 Trusted Advisor

    Location:
    Gliese 581C
    Rod not necessary
    Whats the score with the 2 Rcds?
     
    • Agree Agree x 3
  3. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    Why not swa from board to board
     
    • Agree Agree x 2
    • Like Like x 1
  4. TJ Anderson
    Offline

    TJ Anderson Trusted Advisor

    Location:
    Derby
    More fun at testing time? "Which is gonna trip" lol
     
    • Like Like x 1
    • Funny Funny x 1
  5. Strima
    Offline

    Strima Electrician's Arms

    Location:
    St Neots
    What’s the earthing arrangement at source?

    Have you spoken to your CPS tech helpline?
     
    • Optimistic Optimistic x 1
  6. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    How is the 6.0mm T & E run?
     
    • Like Like x 1
    • Optimistic Optimistic x 1
  7. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    Why are we assuming the OP is in CPS scheme?
     
    • Like Like x 1
  8. Strima
    Offline

    Strima Electrician's Arms

    Location:
    St Neots
    I’ve got nothing better to do tonight.
     
    • Funny Funny x 3
  9. TJ Anderson
    Offline

    TJ Anderson Trusted Advisor

    Location:
    Derby
    That helpline is technically only to help them obtain payment from a bank account!
     
    • Like Like x 2
    • Old Old x 1
  10. Tim collins
    Offline

    Tim collins EF Member

    Location:
    London
    From fuseboard clipped in ceiling void then into cupboard and in trunking before drilling hole outside and terminating to armoured in a wiska box ( client doesn’t want any chasing )
     
    • Creative Creative x 1
  11. Tim collins
    Offline

    Tim collins EF Member

    Location:
    London
    The earthing arrangement is pme , in process of joining cps scheme tried ringing for advice and they said they can’t give me any advice as not member yet
     
  12. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    What scheme is that? Whenever I rung Elecsa tech helpline, they never asked me anything to verify membership.
     
    • Agree Agree x 1
  13. essex
    Offline

    essex Trusted Advisor

    Location:
    Wiltshire
    You almost got a 'dumb' from me then.
     
    • Funny Funny x 1
  14. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    Well done for responding ..... So many don't or simply get stroppy
     
    • Like Like x 3
  15. Flanders
    Offline

    Flanders Regular EF Member

    Location:
    Tamworth
    As Mudroch and Des mentioned don't install two30ma Rcds in line with each other and why use T&E how are you running it outside ?, I Would use Swa and so there will be no nead for a rcd at the supply end
     
    • Like Like x 1