I work for a large telecoms company in the UK, and we have a/c power that is supplied by local dno to our street cabinets. part of the stipulation is the earth rod reading should be below 150 ohms. these rods are tested and fitted by contractors, then their electrician does the electrical testing and certification, but recently we've had an earth rod that was tested in the normal way and has a reading below 150 ohms.but when tested by a megger to get a RA.reading it's way over the 150 ohms, nearly double the value. we've tried. condecrete, earth mats, extra earth rods and it doesn't lower the reading, i've never come across this before. there's other cabinets in the area , same type of soil but these were installed with no problems.
any idea's as to why there should be such a difference, and a solution if any
thanks
 
The Ra readings of an earth rod will change over time and also seasonally, over time they generally improve as the earth compacts around the rod but seasonally they could get worse as the water table changes etc. If the Ra is too high then I'd suggest coupling a new rod on top of the existing one and whacking it in a couple of meters deeper if possible.
 
Just to clarify, you have an earth electrode which had an Ra below 150 when installed but now it has a reading above 150?

How long between the two measurements of Ra and what were the exact figures?
 
I would also ask,by what method was it tested,and was it in isolation,ie where was it tested?
 
I work for a large telecoms company in the UK, and we have a/c power that is supplied by local dno to our street cabinets. part of the stipulation is the earth rod reading should be below 150 ohms. these rods are tested and fitted by contractors, then their electrician does the electrical testing and certification, but recently we've had an earth rod that was tested in the normal way and has a reading below 150 ohms.but when tested by a megger to get a RA.reading it's way over the 150 ohms, nearly double the value. we've tried. condecrete, earth mats, extra earth rods and it doesn't lower the reading, i've never come across this before. there's other cabinets in the area , same type of soil but these were installed with no problems.
any idea's as to why there should be such a difference, and a solution if any
thanks

Some thoughts

1/ It maybe that the previous tester was having a bad day

2/ What type of concrete were you using?

3/There maybe a line of rock or deep gravel across the path of the Ra back to the Tx
 
The measurements were taken at the same time, one with a ground tester used by the contractors, the other with a megger , this reading was taken at the cut out , so it seems when an Ra test is done using 240 power the reading goes up by over 100 ohms.
 
The measurements were taken at the same time, one with a ground tester used by the contractors, the other with a megger , this reading was taken at the cut out , so it seems when an Ra test is done using 240 power the reading goes up by over 100 ohms.

A megger what? Megger is a company who make all manner of test equipment. Megger is also the common name for an insulation resistance and continuity tester.

All earth rod tests will measure Ra. Ra is the symbol used to represent the resistance to earth of an earth electrode, it is not a type of test or test method.

Presumably what you are trying to say is that the rod was tested by a three wire fall of potential test and also the rough approximation method of using an earth fault loop impedance tester. It is normal to get different results with these tests as the three wife test will give you Ra whereas using the earth fault loop impedance will give you Zs.

Can you confirm with a diagram exactly how the installation is set up and where the earth rod connects in to the system? It may be that by using the efli test you aren't testing the earth rod at all,but are in fact testing the suppliers installation (with a fault in it)
 
A megger what? Megger is a company who make all manner of test equipment. Megger is also the common name for an insulation resistance and continuity tester.

All earth rod tests will measure Ra. Ra is the symbol used to represent the resistance to earth of an earth electrode, it is not a type of test or test method.

Presumably what you are trying to say is that the rod was tested by a three wire fall of potential test and also the rough approximation method of using an earth fault loop impedance tester. It is normal to get different results with these tests as the three wife test will give you Ra whereas using the earth fault loop impedance will give you Zs.

Can you confirm with a diagram exactly how the installation is set up and where the earth rod connects in to the system? It may be that by using the efli test you aren't testing the earth rod at all,but are in fact testing the suppliers installation (with a fault in it)


I would change that,fella,or the missus might avoid you,when you have a test machine handy...

Total agreement over the remainder :tounge_smile:
 

Reply to earth rod readings. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
1K
Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area...
Replies
1
Views
423
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Hi All, My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our...
Replies
8
Views
473

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock