I work for a large telecoms company in the UK, and we have a/c power that is supplied by local dno to our street cabinets. part of the stipulation is the earth rod reading should be below 150 ohms. these rods are tested and fitted by contractors, then their electrician does the electrical testing and certification, but recently we've had an earth rod that was tested in the normal way and has a reading below 150 ohms.but when tested by a megger to get a RA.reading it's way over the 150 ohms, nearly double the value. we've tried. condecrete, earth mats, extra earth rods and it doesn't lower the reading, i've never come across this before. there's other cabinets in the area , same type of soil but these were installed with no problems.
any idea's as to why there should be such a difference, and a solution if any
thanks
any idea's as to why there should be such a difference, and a solution if any
thanks