Discuss Earth rods and outbuildings in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
0
Came across an existing TNS installation with earth rod fitted presumably no cable sheath earth and 100ma s type as main incomer and 30ma trip for rest of circuits.
The out building is fed via 30ma and cable enclosed in steel conduit which seems to provide the earth in outbuilding so earth loop is very high, and to add to the mix there is a water supply in the out building.
Should another earth rod be installed for the outhouse and disconnect existing earth supply from house rod?
Thanks in advance
 
might be an idea to use the existing earthing arrangement and add a rod at the outbuilding. i'd maybe call that TN-S/Tel.
 
Don’t have to necessarily.
How far from the house is the outbuilding?
If it’s a long way, then it might be better to use separate rods so as to reduce any differences in potential.
Don’t necessarily have to disconnect the house earthing from the outhouse, could just add a rod at the outhouse and perhaps improve the Zs overall.
 
Don’t have to necessarily.
How far from the house is the outbuilding?
If it’s a long way, then it might be better to use separate rods so as to reduce any differences in potential.
Don’t necessarily have to disconnect the house earthing from the outhouse, could just add a rod at the outhouse and perhaps improve the Zs overall.

What would you say is an acceptable distance to an outhouse/shed before you would install an earth rod (disregard Zs figures, just curious on what distance you would find to be reasonable without calculating figures etc.)
 
What would you say is an acceptable distance to an outhouse/shed before you would install an earth rod (disregard Zs figures, just curious on what distance you would find to be reasonable without calculating figures etc.)

That question has no answer. In actual fact I would love to know your reasoning behind such a qurstion.
 
That question has no answer. In actual fact I would love to know your reasoning behind such a qurstion.

If i don't ask the questions then how will I learn, it's why I follow this forums posts; I wasn't trying to come across as being funny, i just figured someone might know something I don't
 

Reply to Earth rods and outbuildings in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
293
I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
Replies
3
Views
296
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
535

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock