Discuss Earthing and Bonding sizing. in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
19
Morning All,

Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC.
Earthing is TNS with main bonding requirements being 25mm2.
Using table 54.7 - CPC is half of line conductor so 35mm2.

Am I correct in thinking the 35mm2 conductor is adequate for both CPC and bonding requirements?

Cheers guys.
 
Morning All,

Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC.
Earthing is TNS with main bonding requirements being 25mm2.
Using table 54.7 - CPC is half of line conductor so 35mm2.

Am I correct in thinking the 35mm2 conductor is adequate for both CPC and bonding requirements?

Cheers guys.
Good morning,

That’s looking good, could probably manage smaller if you did Adiabatic but that’s on the safe side I guess.

So for 70mm² line if you select from the book it has to be (S / 2) so that’s your 35mm² main protective conductor. Then main bonding should be no less than half the main earth but need not exceed 25mm².

If I’ve missed anything let me know but all looks good to me.
 
The SWA of 4 core 70mm is 138mm² the equilalent in copper is 61mm², therefore the armour is big enough on its own.

Copper has a conductivity 8 times that of steel, so 138mm steel is equivalent to 17mm copper. So no, the armour is not sufficient to meet the requirements for bonding.

I think you may he confusing the calculation for suitable size of steel CPC with that for working out the 'copper equivalent' for the purposes of bonding.
 

Reply to Earthing and Bonding sizing. in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
resitting Saturday my am2 4 sections a3/b/d/e swa and sy failed on protective conductors on both swa i under stand thats the earths i...
Replies
1
Views
1K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
601
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock