- Reaction score
- 25,471
Don't understand the question.
Discuss Earthing and bonding in the UK Electrical Forum area at ElectriciansForums.net
I had not heard this ... I look in BYB section 312.2.1 fig 3.9 where TNCS and PME seem to be the same thing (?).Not all TNCS supplies are PME but all PME supplies are TNCS so how do you know if it's PME, will the DNO always put a sticker on?
Quite simple.I see now, don't see relevance of question though.
In this case then, what's to stop you using a 4C 10mm SWA (even if you don't need one), and using the 4th core for the Bonding conductor?These cables would be used for supplies to other buildings where bonding would be required, the size of main bonding has already been decided at the DNO source. We are not discussing DNO supply cables.
Nothing.In this case then, what's to stop you using a 4C 10mm SWA (even if you don't need one), and using the 4th core for the Bonding conductor?
Lol.These cables would be used for supplies to other buildings where bonding would be required, the size of main bonding has already been decided at the DNO source. We are not discussing DNO supply cables.
Are you trying to get a rise or are you just not understanding.Lol.
What does that mean?
Are you suggesting that this supply to another building would be larger than the DNO supply at source?
length of run ,volt drop earth loop imp. etcI think it is you that is having a problem with understanding.
If the main incomer requires 10mm2 bonding conductors, that would suggest the supply conductors are no greater than 35mm2.
Why would you then use 95mm2 SWA for a sub main?
I have no idea why you keep referring to the supply conductor size, the point is can a sub main swa cable support bonding when the armour is used as the earth. This will nearly always apply to a three phase supply where the minimum size to support bonding would be 50.0. In this day and age people nearly always use three core cable utilising a core as the cpc for single phase supplies. Otherwise it would have to be 95.0 for a two core.I think it is you that is having a problem with understanding.
If the main incomer requires 10mm2 bonding conductors, that would suggest the supply conductors are no greater than 35mm2.
Why would you then use 95mm2 SWA for a sub main?
Reply to Earthing and bonding in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.