of course they haven't Badged01!!

I thought though that the last N/E join had to be actually at the head, not somewhere in the road!!
 
All they have done is earthed the neutral at the road joint, if the lead sheathing is still good, then treat as a TN-S system. If not, then get the buggers back to officially convert the head to a PME supply....

I'd hazard a guess that most of all old TN-S local network distribution cables have had bad sections PME'd., thus leaving these cable carrying both TN-S and TNC-S
 
All they have done is earthed the neutral at the road joint, if the lead sheathing is still good, then treat as a TN-S system. If not, then get the buggers back to officially convert the head to a PME supply....

I'd hazard a guess that most of all old TN-S local network distribution cables have had bad sections PME'd., thus leaving these cable carrying both TN-S and TNC-S

I bet you're right! All this 'investment' that the increasing bills are meant to pay for and we still have ancient cables, some DNOs who won't fit isolators, and the whole issue of safe disconnection...

Another beer vicar?
 
All they have done is earthed the neutral at the road joint, if the lead sheathing is still good, then treat as a TN-S system. If not, then get the buggers back to officially convert the head to a PME supply....

I'd hazard a guess that most of all old TN-S local network distribution cables have had bad sections PME'd., thus leaving these cable carrying both TN-S and TNC-S

I was chatting to a DNO bloke a couple months ago. He was there to change an old head for a new one. It was a TNS. He said to me something along the lines of "you have lots of different names for things, we just call them TT or PME. This one we would call a PME"
He told me that everytime they have a fault on a cable that needs to be dug up and fixed, they PME it.
 
I was chatting to a DNO bloke a couple months ago. He was there to change an old head for a new one. It was a TNS. He said to me something along the lines of "you have lots of different names for things, we just call them TT or PME. This one we would call a PME"
He told me that everytime they have a fault on a cable that needs to be dug up and fixed, they PME it.

He's not correct though is he, at best that statement is very misleading. There are still thousands of network distribution cables that are still TN-S, and have had no PME/TNC-S connections made to them as yet. There are greater number of older TN-S cables that have had PME connections made to them, but are in no way close to being a true PME supply. There are more network distribution cables out there that are carrying both TN-S and TNC-S, than one or the other TN sytems.

The only distribution supplies that can be guarantee'd to be PME when converted, are overhead distribution supplies, when the DNO's ''must'' earth the neutral at every third or fouth pole on the strings...
 

Reply to Earthing at the Origin in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
902
I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
Replies
3
Views
335
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
773
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock