Discuss Economy 7 RCCB Trips from 24hr Circuits Your Thoughts in the UK Electrical Forum area at ElectriciansForums.net

Pip

-
Reaction score
17
Hi Guys,

Called out yesterday morning client has 2 x Wylex Boards with MCB's each has a 63Amp, 100Ma RCCB as the main switch on a TT System.

Board 'A' is the main 24hr feed for the house, Sockets., Lights etc 8 circuits
Board 'B' is the economy 7 night storage heaters. feeding 7 circuits. Midnight to 7am

A Smart meter has been installed recently, where the neutral is split to feed both boards and of course the 2 live feeds. No issue there I think?

Problem they have had for at least 12 months they tell me, happens more in the winter months, is intermittent tripping on the Board 'B' RCCB when it is not energised.

Most recently one afternoon when they put the kettle on and then a small table light, the lamp blew, which they do, only it tripped the Board 'B' RCCB

OK Live - Neutral imbalance due to the lamp blowing but why Board 'B' and not 'A'

Both Boards are 20+ years old and have a cupboard built around them so getting access to the circuits is difficult without destroying the cupboard.
All I have done is RCD tested x1= 17.3 x5 = 5.0 (I know not a requirement but meter does it) Ramp test at 85Ms. BOTH Boards tripping at the same time during these tests. Should They?
PFC 0.48Ka & 0.47 Ohms at a kitchen socket very close to the boards.

So before I remove the cupboard and make a mess to start IR all the circuits etc. does the panel think its a weak RCCB on Board 'B'?

Board 'B' still live somehow?

I don't have a Earth Leakage Clamp Meter, but reading some posts on here I'm tempted, but I don't a discussion of the pros and cons here, but would it help in this case? if yes why?

Anyway over to you my learned friends.

Thanks
 
Have you had a look through the forum at all of the other threads discussing RCDs tripping when circuits which aren't connected to them are used?
 
Hi DaveSparks,

Yes, some, but finding ones that don't go off topic and relate to this scenario I've yet to find, I'll have to hone my search skills.

Thanks
 
Hint Taken, Yes my thoughts N-E Fault, looks like the cupboard is coming out, may get the client to keep a diary first, and do a little more nosing around the property to see if there is something obvious plugged in that shouldn't be.

Thanks for your hints and help
 
If your thoughts are N-E fault why haven't you tested for this?
Why do you want to waste time looking for something plugged in, unless they have sockets connected to the off peak board that is?
You do actually understand how a N-E fault causes the symptoms you have don't you?
 
Hi,

Have not tested as can not get access to the board as I mentioned it has a cupboard built around it so removing the front cover is not possible.

As you say IR test and I'll nosey around for any DIY picture hanging etc.. And I don't know what they have plugged in anywhere yet but as you say I doubt anything on the off peak

Thanks
 
Looking around for DIY picture hanging, loose floorboards is not the answer, you are jumping around a logical fault finding procedure.
You need to get the C/U front cover off to carry out testing, the testing you have carried out so far are incomplete - insist that your able to remove the cupboard, even if you destroy it.
Ask the customer what is more important to them a safely working electrical installation or the visual appearance of a cupboard.
 
Try this for logic:
You have a N-E fault of some impedance on an off peak circuit. The tripping is worse in winter than in summer.
The off peak circuits supply heaters and an immersion heater.

If you really can't get to the CU without wrecking the house then maybe a quick test of the storage heaters and immersion heater might pay off.
 
If you switch off the main switch for board B then you should have separated neutral and earth for those off peak circuits so you can now do IR testing for the whole board from the heaters themselves and start narrowing down your options.
Splitting down the neutrals for the individual cables will be difficult but at least you can eliminate the heaters if the results come out well.
Presumably your results will be OK on all items and you can then start searching for the cross connection to board A.
 

Reply to Economy 7 RCCB Trips from 24hr Circuits Your Thoughts in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
868
Hi, So I'm trying to understand what's going on with my off-peak electricity supply, as something's wrong with it and I'm trying to determine if...
Replies
5
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
739
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock