Discuss Economy 7 rewiring problem for storage heaters in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

LenGot

DIY
Reaction score
0
I recently got my flat rewired. It had old storage heaters and we plan on putting modern storage heaters in. The way the electrician did the rewiring means that there is only night time supply for the future heaters, although now I’m looking at buying heaters, I realise that all modern heaters need both night and day supply.

My electrician has said to get both supplies to each single socket would mean putting a new cable through all the trunking/in the walls. Or alternatively adding extra sockets next to the night time sockets, that come off the plug circuit.

Is there an easy way at the fuse box end to supply the night time fuse box with both day and night power?

Any suggestions welcome for the best way to solve this problem! Thank you :)
 
TL;DR
Can you change night fuse box to have both day and night power supply?
I recently got my flat rewired. It had old storage heaters and we plan on putting modern storage heaters in. The way the electrician did the rewiring means that there is only night time supply for the future heaters, although now I’m looking at buying heaters, I realise that all modern heaters need both night and day supply.

My electrician has said to get both supplies to each single socket would mean putting a new cable through all the trunking/in the walls. Or alternatively adding extra sockets next to the night time sockets, that come off the plug circuit.

Is there an easy way at the fuse box end to supply the night time fuse box with both day and night power?

Any suggestions welcome for the best way to solve this problem! Thank you :)
I'm not fully up on all the possible options.
If you plan on replacing the storage heaters, then you could use single supply heaters, connected to your new outlets, and the wiring of those outlets would need to be transferred at the consumer unit end to be all 24 hour supplies (which ought to be a fairly straightforward job)
Then you would need a smart meter that switches whole house to off-peak at night (which you may already have).

There may be other approaches.
 
Last edited:
My electrician seemed to think that the transferring of power at the consumer unit end would be more work than the option he gave me.

We don't have a smart meter, but our meter is the kind that switches the rest of the electric from day to off peak mode.

We have two fuse boxes, one for 24hr supple and the other with the heaters, off peak supple. So are you suggesting that wiring the heaters fuse box to have 24hr supply is possible?
 
If you supply the heaters via the 24hr supply then you're relying on setting the off peak charging times within the heater itself. You will need to make sure you match the off peak hours on your tariff. Any mismatch means you're using peak electricity. Be aware that in most cases these remain on GMT, so for example if it's 23:00 to 06:00 (GMT) in Winter, you'll need to change to it to 00:00 to 07:00 (BST) in Summer, or leave it at 00:00 to 06:00 all year round.
 

Reply to Economy 7 rewiring problem for storage heaters in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
856
I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Replies
1
Views
557
Hi, So I'm trying to understand what's going on with my off-peak electricity supply, as something's wrong with it and I'm trying to determine if...
Replies
5
Views
1K
Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
765
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock