Currently reading:
EIC - help please

Discuss EIC - help please in the Australia area at ElectriciansForums.net

Reaction score
1
Hi All

I have just installed a distribution circuit from Farm House to Mobile Home - straight forward job in SWA via Henley block and Switchfuse etc.

The Cut Out was 60A feeding 3036 fuseboard no circuit charts/labels etc typical farm installation.

My qusetion is what do I put in the tick boxes regarding presence of diagrams/danger notices/mixed wiring colours etc. Is it acceptable to put n/a surely I can't be expected to identify & label every circuit of the whole farm house if only installing sub main?

Also other tick boxes regarding routing of cables in prescribed zones?

Thank you
 
Hi All

I have just installed a distribution circuit from Farm House to Mobile Home - straight forward job in SWA via Henley block and Switchfuse etc.

The Cut Out was 60A feeding 3036 fuseboard no circuit charts/labels etc typical farm installation.

My qusetion is what do I put in the tick boxes regarding presence of diagrams/danger notices/mixed wiring colours etc. Is it acceptable to put n/a surely I can't be expected to identify & label every circuit of the whole farm house if only installing sub main?

Also other tick boxes regarding routing of cables in prescribed zones?

Thank you

cross in the box and mention it in departures
 
On the EIC, "Extent of the work covered by this certificate", Distribution circuit from Farm house to Mobile home CU ONLY. You can then tick all the relevant boxes, you shouldn't have any crosses in any boxes if you have installed a new circuit, just ticks and N/A's. As long as your work is compliant, then all is well. You have no responsibility for the circuits coming out of the mobile home CU.

Cheers.......Howard
 
On the EIC, "Extent of the work covered by this certificate", Distribution circuit from Farm house to Mobile home CU ONLY. You can then tick all the relevant boxes, you shouldn't have any crosses in any boxes if you have installed a new circuit, just ticks and N/A's. As long as your work is compliant, then all is well. You have no responsibility for the circuits coming out of the mobile home CU.

Cheers.......Howard

Thankyou - that makes more sense, I distinctly remember reading that NO crosses or LIM's should be on an EIC only PIR's - yes all my work on SM is compliant.
 

Reply to EIC - help please in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock