Discuss EICR and outside lighting in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Jacko

-
Reaction score
17
Hello,

How would you go about testing outside lights on an EICR if they are supplied off an outside socket?

The sockets are supplied off the downstairs ring main, inside there is a 13amp switched fuse spur, then a double pole isolator running outside to 3 x double outdoor sockets all run in SWA. There is a ‘Knightsbridge remote control lighting switch’ inside a weatherproof box plugged into one of the sockets and that supplies 5 x lights fitted on the wall.

All SWA glands are fitted correct supplying the sockets, hi tuff cable is used for supplying the lights, all adaptable boxes and light fittings are correctly IP rated.

The lights can be unplugged (if you remove a small decking board) so would they be included in the test?

Thanks.
 
test up to and including the sockets. anything plugged in is outside of your remit.
 
As outside lights can be a potential source of danger, I would include them in the EICR.
They fall under Part P in any case. Not notifiable works necessarily, but part P covers all work in dwellings. Even if wired via a plug and socket.
 
This is the same sort of question from an earlier “entire conservatory wired from a plug top”

I think,if it’s wired as a permanent installation, such as part of it in SWA, then it’s gets tested.... and if it’s a single or group of say, under unit lighting on a plug, then no... don’t test it.
 

Reply to EICR and outside lighting in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
534
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
832
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K
Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
544

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock