The fact it is accessible to the public is irrelevant. If the existing protective device satisfies ADS there is no requirement for RCD protection. No Code required.
 
714.411.3.4 Additional protection
Lighting that is accessible to the public shall have additional protection by an RCD having the characteristics specified in Regulation 415.1.1
Examples include:
1. Gardens, spaces open to the public
2. Telephone kiosks
3. Bus shelters
4. Advertising panels and town plans
This list is not exhaustive.
The following are excluded:
5. Street lighting and traffic signage
6. Illumination of monuments
7. Platform lighting at rail/bus stations.

In view of the above quoted regulation, it could be argued that RCD protection is needed for certain types of car park lighting, especially bollards, which are easily damaged by cars and vandalism. However, in terms of coding for an EICR, a judgement would have to be made by the inspector, based on the assessment of the risks to the public. I can't help but relate this to the infamous pub incident a couple of years ago, where RCD protection could well have saved a child's life.
 
714.411.3.4 Additional protection
Lighting that is accessible to the public shall have additional protection by an RCD having the characteristics specified in Regulation 415.1.1
Examples include:
1. Gardens, spaces open to the public
2. Telephone kiosks
3. Bus shelters
4. Advertising panels and town plans
This list is not exhaustive.
The following are excluded:
5. Street lighting and traffic signage
6. Illumination of monuments
7. Platform lighting at rail/bus stations.

In view of the above quoted regulation, it could be argued that RCD protection is needed for certain types of car park lighting, especially bollards, which are easily damaged by cars and vandalism. However, in terms of coding for an EICR, a judgement would have to be made by the inspector, based on the assessment of the risks to the public. I can't help but relate this to the infamous pub incident a couple of years ago, where RCD protection could well have saved a child's life.
Yes the bollards are regularly knocked over by vehicles 🙄

sometimes the cabling is exposed until I get the call to get there and repair them
 
There was a lamppost totalled at the local Macdonalds car park. Sat with just the stump, a few traffic cones in the 4 spaces around it and some barrier tape for 6 months until they fixed it over Xmas.

Someone’s flattened it again…. Timber!
Coned off 6 spaces now.


Nothing to add to the thread… just a silly story
 
This was added in amendment 2 2022 , i would code this as a C2 , we code to the latest regulations. From a practical point of view I try to asses the danger ,which in this case could be quite high , as stated cars run them over they are also subject to weather, water ingress ,freezing ,heating , i would not like to touch one in the rain especially if the cpc was corroded and the insulation deteriorated.
 
This was added in amendment 2 2022 , i would code this as a C2 , we code to the latest regulations. From a practical point of view I try to asses the danger ,which in this case could be quite high , as stated cars run them over they are also subject to weather, water ingress ,freezing ,heating , i would not like to touch one in the rain especially if the cpc was corroded and the insulation deteriorated.
Yes I agree

The bollards are also around footpaths and in the grassy areas of the flats where the kids play around in the summer

If one is knocked over it’s not hard to imagine an inquisitive child messing about with it
 
This was added in amendment 2 2022 , i would code this as a C2 , we code to the latest regulations. From a practical point of view I try to asses the danger ,which in this case could be quite high
Yes, we code to the latest regs, and one of those regs is that if the installation was compliant when fitted, but not now, although still in good condition, then the code is C3.
Yes, the potential danger is very high, which is why I would endorse the C3 with a strong written recommendation that it is upgraded, transferring responsibility to the owner of the equipment.
 
one of those regs is that if the installation was compliant when fitted, but not now, although still in good condition, then the code is C3.

No it isn't, there is no such regulation.

There is a note which says that something installed to previous regs may not necessarily be unsafe. The key point is 'not necessarily' which means that it may or may not be unsafe.
 

Reply to EICR code car park lighting in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
603
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Hi everyone Sorry if it's a repeated question tho. Agents followed me a failed visual EICR which has C2 for lack of RCD on cooker circuit and...
Replies
11
Views
1K
Morning, Company had an external contractor coming in to complete an EICR recently. They have gave us the report with a C2 for holes in trunking...
Replies
22
Views
3K
Question is does this DB really need RCD protection as there are only internal lights and sockets supplying this large building that used to be a...
Replies
13
Views
569

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock