Hi guys,

just looking for some advice on a few common issues ive found when conduction a commercial EICR and how best code them. Any advice and help is much appreicated.

So hear are some the senarios

1. No fuse spur to heater (hard wired straight to MCB with correct size cable and MCB for heater)- Im thinking code 2?

2. No isolator/fuse spur to curtain heater (hard wired straight to MCB with correct size MCB and cable for curtain heater in question) - again code 2?

3. Missing lid that covers MCBs (not fuse board cover) Code 3?

4. Different manufacture MCBs in board. (e.g 12 way wylex board with 11 wylex MCBs and 1 hager MCB) code 3?

5. Cables not supported in their runs? code 2

6. Cables not supported above false ceiling and lying on metal frame work. code 2?

7. Emergency lights not wired correctly for testing - just info

8. Main service incomer in open with no cupboard or barrier - code 2 with recommendation of some sort of cupboard or barrier.

9. DB in open with no cupboard or barrier - code 2 with recommendation of some sort of cupboard or barrier added to cover DB.

10. No visable signs of supplementary bonding - If it looks like it could be covered in building fabric and able to obtain a very low resistance reading with a wander lead then - info with notes

11. Breakers such as 3871? code 3 recommend upgrade to 60898 breakers

12. Old board with 3871 breakers with half upgraded to 60898 breakers - code 2 with recommend the rest upgrade to 60898s.

13. Fire panel not wired from DB to fire panel in fire resistant wiring - code 2.

14. No main switch between incomer and DB or first DB - code 2 if commercial

15. RCD as main switch on DB - code 2 with recommendation of main switch added even if it means a board change a no spare ways

if anyone would like to add to this list it may be helpful for others including myself.
 
Last edited:
you need to consider each point and ask your self if you consider that there is a potential danger or not. if yes, then it's a code C2. if not, then C3.
 
Hi guys,

just looking for some advice on a few common issues ive found when conduction a commercial EICR and how best code them. Any advice and help is much appreicated.

So hear are some the senarios

1. No fuse spur to heater (hard wired straight to MCB) - Im thinking code 2?
What size heater, what size MCB, what size cable ?
2. No isolator/fuse spur to curtain heater (hard wired straight to MCB) - again code 2?
As above
3. Missing lid that covers MCBs (not fuse board cover) Code 3?
Which reg are you stating here ?
4. Different manufacture MCBs in board. (e.g 12 way wylex board with 11 wylex MCBs and 1 different make MCB) code 3?
Which reg are you stating here ?
5. Cables not supported in their runs? code 2
What is the situation and location and what is the perceived danger ?
6. Cables not supported above false ceiling and lying on metal frame work. code 2?
What type of cable, what situation, what danger are you commenting on ?
7. Emergency lights not wired correctly for testing - just info
?
8. Main service incomer in open with no cupboard or barrier - code 2 with recommendation of some sort of cupboard or barrier.
Which reg are you stating here ?
9. DB in open with no cupboard or barrier - code 2 with recommendation of some sort of cupboard or barrier added to cover DB.
Which reg are you stating here ?
10. No visable signs of supplementary bonding - If it looks like it could be covered in building fabric and able to obtain a very low resistance reading with a wander lead then - info with notes
Is the bonding needed ?
11. Breakers such as 3871? code 3 recommend upgrade to 60898 breakers
Which reg are you stating here ?
12. Old board with 3871 breakers with half upgraded to 60898 breakers - code 2 with recommend the rest upgrade to 60898s.
Which reg are you stating here ?
13. Fire panel not wired from DB to fire panel in fire resistant wiring - code 2.
Which reg are you stating here ?
if anyone would like to add to this list it may be helpful for others including myself.

My thoughts in red.
 
im looking for general advice overall not on a particular installation. So basically on the first points id be taking it the right size heater, cable and MCB is in place

So what code would you give it if the co-ordination between cable size, kW rating of heater, and MCB were as they should be for compliance with the regs ?
 
I agree a with ANDY and you seem to be putting code 2s against a lot of observation that are not potentially dangerous , why do you think 3871 MCBs are potential dangerous and it would depend on the environment for barriers around service Head , for example if fork lift truck could hit it then I would agree with a code 2
 
thats why im on here andy to get some guidance and advice.

What code if any would you be inclinded to give a DB that isnt in a cupboard or within any barrier, ect.

I mentioned this in post 7 " it would depend on the environment for barriers around service Head , for example if fork lift truck could hit it then I would agree with a code 2" every installation is different so there is not just one answer to this
 
thats why im on here andy to get some guidance and advice.

What code if any would you be inclinded to give a DB that isnt in a cupboard or within any barrier, ect.

My best guidance and advice would be that if you are not sure whether something is required by the regs or not then look it up in the regs. It's going to take a long time to go through all your original points at this rate.

A lot of your original points would be dependant on the situation and it would be impossible to tell you what code as some could range from no code to a C2 dependant on other factors. It's down to the inspector to deem issues dangerous or not based on the situation, but all observations must have a basis in the regs otherwise it's not a technical report based on the requirements of BS7671, it's just opinion.

If you could answer all my points in red from my first post then we could start from there.

I would also advise some serious revising or studying as you seem to be picking codes at random without any thought or justification as to why. If a client handed me an EICR with all your points coded as they are in your original post I would tell them that someone either didn't know what they were doing, and/or is trying to pull a fast one with a large remedial works bill.
I'm not trying to be harsh with that comment, just offer my truthful opinion.
 

Reply to EICR codes advice in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb. I know...
Replies
8
Views
1K
Hi - we have an inline heater for a vent system that appears to always be on. I believe the electrician may have wired it incorrectly with only a...
Replies
3
Views
686
Evening Gents just after a bit of advice and what would you do differently. I have wired up 3 kw heaters in 4mm tuff cable (40 meter distance...
Replies
2
Views
251
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
578

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock