  1. 1983
    Offline

    1983 Regular EF Member

    Hi guys Advice again please went to carry out A eicr in a flat which is in an estate with about 40 plus flats. in the intake room went to check the condition of the supply 3phase tncs with a separate earth coming in or was coming in seems like somebody cut it off and nicked it phone the dno to let them know they telling to earth rod it spoke to nic after explaing the situation he telling me the install is to big to earth rod and if I could crimp it once I told him it's the suppliers side he saying not to touch for safety reasons which is understandable and that his been in a similar situation and how i need to convince the dno to come out and give a quote to sort out the earth and how i need to know how to word it across to them to convince them to come out. My understanding is seen as the dno have supplied the earth it's there responsibility to maintain it they seem like they not boverd
     
  2. Rpa07
    Offline

    Rpa07 2000 posts - only 46379 behind Telectrix! Electrician's Arms

    Location:
    Bristol
    Business Name:
    Ebenezer electrical
    BREATH MAN! Remember to use punctuation and grammar when coming onto the forum. It helps the members to stay focussed on what your issue is and how they can help. Having said that.........
     
    • Like Like x 3
    • Funny Funny x 2
    • Agree Agree x 1
  3. 1983
    Offline

    1983 Regular EF Member

    Sorry mate
     
    • Like Like x 2
  4. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    does, or did, the main earthing conductor come from the service head? if so, then it's not DNO's responsibility after the service head.
     
  5. Rpa07
    Offline

    Rpa07 2000 posts - only 46379 behind Telectrix! Electrician's Arms

    Location:
    Bristol
    Business Name:
    Ebenezer electrical
    And ALWAYS snap some photos - picture paint a thousand words (with or without the commas)
     
    • Like Like x 1
    • Agree Agree x 1
    • Funny Funny x 1
  6. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    Are you saying that 40 Flats are without any form of earthing? Who are you doing the EICR for?
     
  7. 1983
    Offline

    1983 Regular EF Member

    I'll get pics when I next there sometime next week hopefully. the install has an earth strap coming off the services heads neutral connected to the trunking which has all tails runing through it but there was a separate earth also coming out the floor next to the supply which was connected to the neutral link which has been cut. Am I right thinking that the separate earth coming in was like a back up if neutral was lost on the dno side? I got good zdb reading within the flat tho
     
  8. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    could it have been to a rod that was dissed when PME was installed?
     
  9. 1983
    Offline

    1983 Regular EF Member

    Is it possible? Nic told me that a install that big can't be earth roded. At 1st he told me to crimp it then asked if it's on suppliers side or consumer side told him it comes out the ground next to main incomer then he goes not to due to a possible fault while trying to crimp it and that his been in a similar situation and how dno came out disconnected supply to Carrie out works. With new 18th coming out and talks about earth rods with tncs systems got me thinking was this a separate earth run by dno in case lost of neutral
     
  10. 1983
    Offline

    1983 Regular EF Member

    I'll see if i can pop over tomarrow to get some pics if not next week. Thanks guys as always appreciate everyone's time and effort for helping out
     
  11. 1983
    Offline

    1983 Regular EF Member

    The earth is cut from ground where reachable to the link coming out the dno neutral
     
  12. 1983
    Offline

    1983 Regular EF Member

    But inside the trunking there's an earth strap to it from the neutral so has an earth still but just this cut off separate earth coming in is what I'm thinking looks like it's been nicked
     
  13. Leesparkykent
    Online

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    You sure the cut one isn't a bonding conductor for the likes of lightning protection etc?
     
  14. 1983
    Offline

    1983 Regular EF Member

    Its not a high rise building
     
  15. Leesparkykent
    Online

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    I've just done a block of flats that's 5 floors and it has lightning protection.

    IMG_0961.JPG
     
  16. 1983
    Offline

    1983 Regular EF Member

    I'll post some pics when I get the chance to go there next but is it not the dno responsibility seen as it goes in to there neutral
     
  17. 1983
    Offline

    1983 Regular EF Member

    I'll post some pics when I get the chance to go there next but is it not the dno responsibility seen as it goes in to there neutral
     
  18. Leesparkykent
    Online

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    I don't really get your 1st few posts...didn't realise it was connected to the neutral I just thought you had a green and yellow that come out the floor and it's been cut.
     
  19. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Could be to a rod as it is PME there is a requirement to stake it at intervals to limit the resistance to true earth, have you tried a loop test to it. Me I would comment in the Report and only worry if remedial works are required.
     
  20. 1983
    Offline

    1983 Regular EF Member

    Remedial works are required within the flat. Good zdb reading in the flat tho I was thinking that as well pme earth rod would that not be a c2?
     
  21. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
     
  22. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    You don't know it is a rod or its purpose if any so without these facts you need to use your own judgement as to whether the safety of the installation is being compromised.
     
  23. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    I'm a bit lost - flat has good Zdb, so why get DNO involved ? What have I missed ?
     
  24. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    I missed Eastenders.
     
    • Funny Funny x 1
  25. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    I'm lost, you've said the main earth has been cut off, and also that there is a strap connecting to a PME terminal in the trunking???
     
  26. 1983
    Offline

    1983 Regular EF Member

    The main incomer has a separate earth coming in with it which was connected to the neutral on the supply head which has been cut of but when I opened the trunking lid I could see an earth strap off the trunking going in to the neutral aswell the system has an earth but was thinking bout the separate one that as been cut
     
  27. jackhammerJIM
    Offline

    jackhammerJIM Regular EF Member

    Location:
    north yorks
    sounds to me like its the first earth rod along the pme network .
     
  28. 1983
    Offline

    1983 Regular EF Member

    That's what I was thinking mate and dno don't wana know nic telling me not to touch as it's before the meters.
     
  29. jackhammerJIM
    Offline

    jackhammerJIM Regular EF Member

    Location:
    north yorks
    Get the DNO out to look at it . It is their back up for a neutral fault .
     
  30. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Did you ever do a loop test to it.
     
  31. 1983
    Offline

    1983 Regular EF Member

    Haven't been back since hopefully next week some time
     