- Reaction score
- 16,689
It's not part of the ring it has its own source.
You need to look at Appendix 15 section A in the regs. It clearly states 'An unfused spur may be connected to the origin of the circuit in the distribution board'.
Discuss EICR - Help on my Request for Electrical Safety Alternatives and Quotes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
It's not part of the ring it has its own source.
You need to look at Appendix 15 section A in the regs. It clearly states 'An unfused spur may be connected to the origin of the circuit in the distribution board'.
It also says that a spur is : a branch from a ring or radial final circuit.
Then in my opinion it's not a spur.
It's not part of the ring it has its own source.
It also says that a spur is : a branch from a ring or radial final circuit.
Appendix 15 is informative, not normative, and therefore does NOT form part of the Wiring Regulations.You need to look at Appendix 15 section A in the regs. It clearly states 'An unfused spur may be connected to the origin of the circuit in the distribution board'.
wow daveboy ,i nearly spat my dinner over the screen ,you are not calling him Mr invisible with long fingers typing away, i cant see you .not the opinion of a faceless stranger on a forum
It's not a radial, it's a spurNot something I would do. What does the radial feed?
I would still argue that there is no question, it is just not an accurate description of the problem.As I said it is questionable and my query was perfectly correct.
OK, point taken. Depending on installation method, it may be OK.For you to suggest a 2.5 on a 25A protective device is fine without knowing the installation method is, well, questionable.
It being the typical device protecting an RFC. It could be a C32, but most likely a B32.Not sure how the 32A protective device being type B is relevant.
I would still argue that there is no question, it is just not an accurate description of the problem.
OK, point taken. Depending on installation method, it may be OK.
It being the typical device protecting an RFC. It could be a C32, but most likely a B32.
Presumably we can agree that a 32A MCB (whether B, C, or D curve) protecting a 2.5mm T&E (most likely type of cable) is not acceptable other than certain circumstances (such as being a spur feeding just a double socket) ? So if there is indeed a radial circuit (i.e. something that doesn't meet the requirements to exceed the normal protective device limit for the cable & installation method)) rather than a spur taken off at the MCB, and it's wired in 2.5mm T&E, then that is incorrect - but not because it's sharing an MCB with an RFC. It's incorrect because the MCB rating is too high for the rating of the cable and hence the fault description is simply wrong.
Do we agree that (assuming the cable and installation method agree), having a radial off (say) a B20 would be OK ? Also, having an RFC off a B20, while unusual, would be OK ? Now show me a reg that says they cannot share the same MCB ?
So the description is incorrect, and the statement of "needed" remediation later posted by the OP is incorrect as a result. Moving it to an additional MCB (16A seems a bit low, but as you say, we don't know all the details) is one way of dealing with it, it's not the only way and the wording is incorrect in that respect as well - but that is perhaps being a bit pedantic. For instance, if there is another circuit with a suitably rated MCB, and anticipated usage doesn't suggest it causing problems, then it may be as simple as moving the radial to share a different MCB - and that's probably what most of us would do if there wasn't room in the board to add another circuit.
Given that the inspecting electrician gets this wrong, what else has he got wrong ?
It’s not a spur it’s a radial as stated in the report from the electrician who has actually looked at the install.No it doesn't, it all comes from the same source.
The ring and the spur are all connected to the same OCPD, therefore it is all the same circuit.
Nobody is saying any different.Yes and that branch can be connected anywhere in the circuit.
A spur can be connected to any part of a ring circuit, either at a point , a joint box in the cable or at the OCPD.
It’s not the opinion of a faceless stranger it’s the opinion of a faceless stranger who has actually looked at the install and wrote a report deeming it to be a radial fed from a 32 amp ocpd hence the c2.Great, but that is not what it says in the regulations or the supporting publications. An EICR should be carried out in accordance with the regulations, not the opinion of a faceless stranger on a forum.
It’s not a spur it’s a radial as stated in the report from the electrician who has actually looked at the install.
It’s not the opinion of a faceless stranger it’s the opinion of a faceless stranger who has actually looked at the install and wrote a report deeming it to be a radial fed from a 32 amp ocpd hence the c2.
Nobody is saying it can't be, my point is that when a (spur) is taken from the ring final's ocpd rather than from a point on that ring, it's more like a radial.
If the ring was cut, would this then be 3 radials ? or 3 spurs ?
My post was in relation to the report posted by the op.That post was a reply to your statement that in your opinion a spur from the MCB is not a spur.
You appeared to be implying that in your opinion a spur cannot be taken from the MCB of a ring circuit. I was replying to that saying that an EICR should be carried out to BS7671 and not to your opinion.
Reply to EICR - Help on my Request for Electrical Safety Alternatives and Quotes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.