Just your thinking on this… Doing Remedials on a EICR … the DB is a old Wylex with MCB”S/RCD
Its a 10 way… rammed packed with cabling,,,the Neutral/Earth connections are a nightmare to get at.
The IR measurements are not good coming in around 0.154 MOhms.
I'm hesitant in actually disconnecting all conductors & individually testing them.
Could recommend a new DB & start from scratch…or do it the hard way…anyone?
 
You only need the neutral conductors for an IR test shouldn't be that difficult the neutral bar should be quite accessible.
 
Just your thinking on this… Doing Remedials on a EICR … the DB is a old Wylex with MCB”S/RCD
Its a 10 way… rammed packed with cabling,,,the Neutral/Earth connections are a nightmare to get at.
The IR measurements are not good coming in around 0.154 MOhms.
I'm hesitant in actually disconnecting all conductors & individually testing them.
Could recommend a new DB & start from scratch…or do it the hard way…anyone?
May be worth disconnecting at the MCB and trying to trace which line paired with each neutral (I am thinking with twin an earth) you may be able to see the line go back into the outer insulation and try see where the neutral is terminated in the neutral bar.

I can understand your hesitation if the board is like Spaghetti Junction though, I can be really time consuming taking conductors out to individually test each circuit when they are jam packed into the board.

If you did take a few of the pairs out of the MCB, Neutral Earth bar, you may be able to put them back neater, so that the remaining ones are easier to test without having as much of a struggle trying to identify which cables are for each circuit?
 
Just your thinking on this… Doing Remedials on a EICR … the DB is a old Wylex with MCB”S/RCD
Its a 10 way… rammed packed with cabling,,,the Neutral/Earth connections are a nightmare to get at.
The IR measurements are not good coming in around 0.154 MOhms.
With readings like that you most likely have an appliance still plugged in.Or there is a fixed appliance still in circuit . Its very difficult nowadays when carrying out EICR,s to have 100% of the circuits"clean".Invariably our low IR readings gradually improve as we isolate the "offending" appliance.Does cost an awful lot of time though.
 

Reply to EICR & IR Testing so many cables in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
644
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
842
A recent EICR turned up a fault: an RCD fused spur was feeding a socket and a shower pump, and neither socket or pump had continuity on the CPC...
Replies
17
Views
3K
Did a check on a ring circuit, due to board having to remain live I did it at a socket.. Was an RCBO, had checked RCD side and all tested ok...
Replies
3
Views
1K
Doing some testing today on a Wet Room installation. Fed from its own small CU. And consists of 2 x seperate 50A (for 10.5kw shower) circuits...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock