Search the forum,

Discuss EICR item 4.6 Presence of Main Linked Switch. Is an RCD acceptable? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

L

LeighSawczyn

Hi All,

Does a BSEN61008 RCD fulfill the requirements of 537.1.4?
There is no other means of isolation, the tails come from the meter straight to the single 100A 30mA RCD protecting all circuits via BSEN60898 MCB's in a TT installation.
 
nowt wrong with that. it's a single point of isolation. only thing is that from 2008 (17th), you have no division of circuits between 2 or more RCDs.
 
Thanks Archy & Telectrix.
That's the problem with having an electronic copy of BS7671 one tends not to flick through the pages as you do in a book. If I'd looked in the book properly I would have seen table 53.4 on the previous page. DOH!
 
The requirement to divide an installation into circuits pre dates the 17the edition.

i meant division of circuits between 2 or more RCDs, as in a single RCD upfront, if tripping, will isolate the whole installation.
 
but with 16th, buried cables did not require RCD protection, so lighting circuits and some others went on the non-RCD side of the |CU in a split board. thus leaving some of the installation live when the RCD tripped.
 
Tel you made a big thing about the 17th edition requiring that installations be divided into circuits.
The fact is, that the 16th and most likely the 15th had the same requirements.
Also as this is a TT installation, it's very likely that it would had a single up front RCD under the 16th.
 
Last edited by a moderator:
You can recommend such, however there is no requirement for such work to be carried out.
The current installation complies with the current Regulations, it's just that it's not ideal.
 

Reply to EICR item 4.6 Presence of Main Linked Switch. Is an RCD acceptable? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
907
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
961

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top