Discuss EICR LOCAL BONDING FLATS in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
1
I’m sure this has been covered a squillion times before but advice please. EICR on block of 5 flats all with separate electrical supplies & meters. One boiler serving hot water via one system to all flats. Main bond to water and gas on entry to building. There is no bonding locally within the flats from the flats DB . C3 for no local bonding as shared water / gas supply? Or C2 as the zone within the flat itself needs dedicated local bond. Thanks
 
I’m not sure any regs have been broken as both gas and water are bonded at point of entry?
Supplementary bonding may be needed locally in each flat depending on RCD protection and presence of anything that needs bonding.
 
I’m sure this has been covered a squillion times before but advice please. EICR on block of 5 flats all with separate electrical supplies & meters. One boiler serving hot water via one system to all flats. Main bond to water and gas on entry to building. There is no bonding locally within the flats from the flats DB . C3 for no local bonding as shared water / gas supply? Or C2 as the zone within the flat itself needs dedicated local bond. Thanks
Good question.

411.3.1.2 gives us:
In each installation main protective bonding conductors complying with Chapter 54 shall connect to the main earthing terminal extraneous-conductive-parts including....

Is the whole building one installation? Or, is every flat, and the distribution/communal areas, each installations in their own right?

I think the latter. I think it's possible, through strategically placed plastic sections in the pipework, and earthing problems in one flat, for pipework to introduce a potential into another. I would like to see bonding in each flat.
 
Good question.

411.3.1.2 gives us:
In each installation main protective bonding conductors complying with Chapter 54 shall connect to the main earthing terminal extraneous-conductive-parts including....

Is the whole building one installation? Or, is every flat, and the distribution/communal areas, each installations in their own right?

I think the latter. I think it's possible, through strategically placed plastic sections in the pipework, and earthing problems in one flat, for pipework to introduce a potential into another. I would like to see bonding in each flat.
 
411.3.1.2 also gives us
"where an installation serves more than one building the above requirement shall be applied to each building"
This helps us a bit with the definition of installation and the possibility it is much bigger than one flat.

While I totally agree a potential could be introduced within the building if the pipework is insulated at any point, I thought the main intent of these regs is preventing introducing a potential from outside the building or exporting a potential outside the building.

I do agree that common sense says each flat would be best off with the services bonded so a C3 doesn't seem unreasonable.

The definition of installation from part 2 -
Part 2 - "Installation - see Electrical Installation"
"Electrical installation - An assembly of associated electrical equipment having coordinated characteristics to fulfil specific purposes"
...not sure that helps much!

Love to hear more views on this though - it's a very interesting question.
 
The NICEIC official view is that each flat should be main bonded inside the flat if there are extraneous parts entering the flat, regardless of whether there is bonding at the source on the ground floor.

Which makes sense, as the requirement for main bonding refers to an extraneous conductive part that is likely to bring a potential (mainly earth potential, but not exclusively) into the installation. A potential could be introduced into the flat from another flat, in certain circumstances, for example if there are insulating sections of pipework in the other flat(s).

In other words, it's better to take the belt and braces approach.
 

Reply to EICR LOCAL BONDING FLATS in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
927
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hello! I've just moved in to a new property with "all electric" heating system and trying to figure it out. The agency/landlord are of no help so...
Replies
1
Views
1K
Evening all. EICR done on ground floor flat all electric no gas, flats built 2006, no rcd protection on circuits 1 to 8 - lighting, kitchen...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock