All - Would appreciate some advise or professional help as I'm facing a £4.5K bill following an EICR which seems to highlight issues that passed just last year's EICR.

First EICR done in March 2021 - Passed with only C3 observations.

Second EICR done - just on advise online before change of tenancy - Failed with multiple C2. The tenancts are due in by end of Month and we are facing a hefty bill. Focus of course is to make it safe for tenants but don't want to be ripped off hence would appreciate some advise or professional help.

1 1.3 Consumer meter tails exposed single insulated inner cores. C2 Meter [March 2021 none highlighted]

Capture 1.JPG

2 . No labels on Earthing Conductor and Main Earthing Terminal. C3 MET

3 4.1 Consumer unit mounted at a height which prevents ease of access for user. C3 Entrance [March 2021 No observation see pic under next point[]

4 4.5 IP rating of consumer unit not to BS 7671:2018+A2:2022. Back and top of Consumer unit has an unused opening exceeding IP2X. C2 Consumer unit [March 2021 reading marked as pass. New Consumer Board was installed 2012/13 when we upgraded the kitchen]
Capture 3.JPG

5 4.6 Consumer unit in a domestic household premises is not metal, located in the sole means of escape for a dwelling area. C2 Entrance [March 2021 no issue highlighted]
Capture 4.JPG


6 4.7 Consumer unit has a crack in the protective device access flap. C2 Consumer unit [March 2021 this was a C3]
Capture 5.JPG

7 4.17 No presence of diagram, charts at or near equipment. C3 Consumer unit

8 6.3 Low values of insulation resistance measured 250V DC test voltage (2.28M/ohm). Degraded di-isoctyl phthalate occurying in all checked sockets (except kitchen circuit) wires and sockets throughout the house. C2 Several locations [March 2021 reading >200MOHM]
Capture 6.JPG

9 6.14Mains smoke/heat alarms not installed. Battery alarms poor condition. Advise install minimum 10 years Mains with battery back-up smoke/heat alarms. C3 Several locations [March 2021 not highighted]


Thanks!!!
J
 

Attachments

  • Capture 6.JPG
    58.7 KB · Views: 7
  • Capture 2.JPG
    27.1 KB · Views: 5
Probably the biggest expense would be rewiring the sockets. Yet the insulation resistance of 2.28M is above the minimum, and so perhaps not strictly necessary at this time. If it is oozing out of any socket faceplates (it sometimes is), they can be replaced in the meantime.

A few other things appear a bit strict or not even relevant. E.g. presence of smoke alarms is outside of the scope of an EICR, though you should of course have them.
 
Probably the biggest expense would be rewiring the sockets. Yet the insulation resistance of 2.28M is above the minimum, and so perhaps not strictly necessary at this time. If it is oozing out of any socket faceplates (it sometimes is), they can be replaced in the meantime.

A few other things appear a bit strict or not even relevant. E.g. presence of smoke alarms is outside of the scope of an EICR, though you should of course have them.
Thanks SJD for the advise. Does that mean I can challenge the C2 on 2.28M?

The leaky plasticizer is only at 2 out of 10 sockets perhaps where direct sunlight has been hitting them - both are near windows.

Thanks.
 
I doubt that the inspector will change his/her outcome of the report.

you can ask but if it were me, I would say something along the lines of the installation is clearly deteriorating and may well deteriorate to the point that it becomes dangerous well before it is next inspected. Therefore it is not suitable for continuing use.

it sounds like a detailed report that someone has spent some time inspecting.
some of the items listed are a little harsh but changing a couple of them is not going to change the overall outcome.

I would get a couple of other quotes for the remedial work and see if the price comes down.
 
1. C2 £45 to terminate so no basic insulation showing.
4. C2 £45 to cover holes.
5. I would put this as a C3
6. C2. Replacement cover (If possible) £70
8. IR results are above 2, so I wouldn't be coding.
It's the green goo that could be the costly part. I would C2 it if there was severe green goo which was either damaging accessories or degrading the cable. Even though 2.28Mohms is acceptable, mixed with green goo it may indicate a breakdown of the insulation of the cables meaning you may need a rewire. I would get two further electricians in to get 2 more quotes.

9. Smoke alarms are not a part of an EICR. I would still make the landlord aware that they legally need them though.
 
1. C2 £45 to terminate so no basic insulation showing.
4. C2 £45 to cover holes.
5. I would put this as a C3
6. C2. Replacement cover (If possible) £70
8. IR results are above 2, so I wouldn't be coding.
It's the green goo that could be the costly part. I would C2 it if there was severe green goo which was either damaging accessories or degrading the cable. Even though 2.28Mohms is acceptable, mixed with green goo it may indicate a breakdown of the insulation of the cables meaning you may need a rewire. I would get two further electricians in to get 2 more quotes.

9. Smoke alarms are not a part of an EICR. I would still make the landlord aware that they legally need them though.
Thanks @HappyHippyDad. I wish you were closer to Reading to do this for us :).

Only two sockets are showing green goo outside and of which only one was looking like coming out from the switch after the inspection was completed. Picture of the main culprit socket below:

Capture 10.JPG

Capture 9.JPG

Capture 8.JPG

Capture 7.JPG
 
Only two sockets are showing green goo outside and of which only one was looking like coming out from the switch after the inspection was completed. Picture of the main culprit socket below:
That is not a good sign.

As above, you might argue over some of the codes but there is no doubt that cable is well beyond its working life. Also it is worth pointing out that this problem with the type of PVC plasticiser causing the degradation of insulation and "green goo" was limited to a period of a few years in the late 60s/early 70s so that wiring is 50+ years old now.

Get a couple of quotes for the remedial work.

The earlier EICR you had clearly did not check in so much detail. Not the news you might want to hear, but sadly just how it is.
 
The meter tails is a 5 minute fix for an electrician , literally just need re-terminating

The hole in the top of the consumer unit is pressed up fairly tight to the ceiling so no real risk of someone shoving their fingers in. You can easily just fill with hole some white mastic bathroom sealant . Likewise the cracked cover isn't really be a C2 as its just the flappy cover, I come across many many consumer units where the plastic flappy cover has been snapped off altogether. I just recommend they find a new cover on Ebay.

Low IR is FI not a C2

Geen Goo is a problem but sometimes the offending cable can be cleaned with a wet wipe and the face plate changed then it becomes a more detailed FI where you want to inspect all the cables and a possible partial re-wire req latter on
 
Mostly trivial stuff, the big ones are low IR and green goo.
From what I can see of consumer unit not all the wiring is 1960's at least.

The wiring for the sockets is now seriously old - and when I see that the two things that matter are the IR reading and presence of green goo. It tends to be 1960's wiring that exhibits this. As said above once you see green goo then it's generally game over the the related wiring. I'd agree that a partial rewire is now required, I'm afraid.

Low IR is FI not a C2
Respectfully disagree there Dusty. I used to think that too but I've been told by a few old-hands that FI is for where we can't establish a result, not for where we don't know why we are getting a result.
 

Reply to EICR Nightmare and Advise in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
I would greatly appreciate if someone could help me understand the following outcomes on an EICR. I am being advised it needs a total rewire but I...
Replies
29
Views
4K
My parents had an EICR completed after a change of tenant in the shop and flat property, this took place March 2021. The summary of the report...
Replies
35
Views
5K
Been asked to do remedials on holiday cottages after recent EICR. Modern consumer units, MK Sentry, but no RCD protection on anything. Bit of a...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock