Discuss EICR Observations in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
362
Would like to get other opinions on the following observations of a property that was rewired 10 years ago:

1) Excessively long ring - r1/rn/r2 = 1.56/1.56/2.48

2) Mismatch of RCBO - Hager RCBO in Legrand CFU with othe rLegrand MCBs
 
If the circuit is for general sockets in a house, and lightly loaded, I wouldn't be massively concerned about volt drop. Not great design though!
 
Why would you be verifying voltage drop on an EICR ? It is not within the general remit or requirements of the regs regarding periodic inspection.
This would be near impossible to do accurately anyway as you would have no idea of the exact length of concealed cables. Backwards working of the resistance values would not be an accurate way to verify the length of the cable in my opinion.
 
I wouldnt be overly concerned with the volt drop and as @kingeri said its poor design but its within zs advantage of ring circuits, have the customers experienced any volt drop related problems.? As for diferent brand of switchgear you could c3 as per manufacturers instructions not followed, but if they all fit soundly with no evidence of damage i wouldnt even mention it, just my opinion.
 
Okay mV/A/m for 2.5mm T&E is 18. If you take the design current as 26A for the RFC (20A at the mid point and the rest evenly distributed to the rating of the OCPD. maximum recommended value of volt drop 11.5V(5%).

18x26x98.3/1000/4= 11.5V.

An r1 value of 1.56 with 2.5 would indicate a ring final circuit length of 214 meters 1.56/0.00728=214

18x26x214/1000/4=25V

section 525 is relevant. If 25Volts volt drop is going to cause a potential danger that impairs the safe functioning of equipment then code 2 IMO. If it doesn't then code 3.

If the RCBO fits perfectly no code and just a comment if its not fitting perfectly then code 3. Code 2 if causing any stress on busbar etc.
 
Re ring length.

I refer to Table 7.1(i) OSG - max length of 32A B type - 106meters.

Loading is not heavy so in practise volt drop shouldn't be an issue, but needs mentioning as far as I'm concerned.

Thanks for comments
 
I would note it on the observations sheet but not code it personally. So long as zs is fine. When I QS test sheets I like seeing that the electrician has put some extra thought into the installation assessment. Rather than seeing blank sections all the time. Pet hate of mine.
C3 the mismatched mcbs.
 
Definitely C3 noncompatible device whether it fits correctly or not.
Depending how poor the fit it could easily make it a C2 (or perhaps a C1 if they have butchered around it to the point where there are now exposed live parts - although this is likely to be recorded separately from the incorrect protective device which has been fitted).
 

Reply to EICR Observations in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
Here's one I wasn't expecting on an EICR. Recently rewired and renovated 2-bed property (2015ish). Having an EICR as a new tenant to move in soon...
Replies
40
Views
17K
I do seem to pick only the weirdest properties to inspect... Victorian terraced house today - with up front RCD to a Wylex fuse board and main...
Replies
24
Views
3K
Hi there, Just hoping something can clear another small item up for me at all. When designing a circuit and looking at cable length for a Ring...
Replies
1
Views
966

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock