Would you guys be happy with these readings on ring main,Rcbo c type 30ma/32 amp.
r1 1.87...rn 1.91 cpc 3.20....R1 +R2.1.26.
zs 1.46 ohms.
 
What size cable is it?....and why a “c” type?....I have no answer to your question but am genuinely interested ?
 
It is quite a long circuit, but from the fact that it is a C32 RCBO, I'm suspecting this is commercial / industrial, rather than domestic? For example, a ring in a large workshop, warehouse, school, etc.

I'd be wondering about the voltage drop, e.g. are all the loads at middle of the ring because the outlets happen to be a long way from the distribution board?

Or has someone used a somewhat too small cable size, e.g. 1.5mm2 T&E or SWA?
 
It’s in a quite a large office area,it’s defo 2.5mm,difficult to judge where the actual loads are,there are mainly,computers plugged in.Been in service @ least 5 years,all signed of.
 
It’s in a quite a large office area,it’s defo 2.5mm,difficult to judge where the actual loads are,there are mainly,computers plugged in.Been in service @ least 5 years,all signed of.
That sounds like most of my customers.....worked fine like that for years ?
 
It’s in a quite a large office area,it’s defo 2.5mm,difficult to judge where the actual loads are,there are mainly,computers plugged in.Been in service @ least 5 years,all signed of.
if that's the case, why not replace MCB with a B type, even drop to a 20A?
 
Sorry to hijack the post but for someone still learning how do you work out the length of circuit from the readings ie what would the formula be please ? Tia
Look in the on-site guide, appendix, I think it's table 11

It gives the R1+R2 resistance per metre

So for 2.5/1.5 it's around 19.5 miliohm per metre if you know the length, it's length x this value, if you know the overall resistance it's the resistance devided by the resistance per metre

You could also work it out from R1 for 2.5mm2 per metre, plus R2 for 1.5mm2 per metre

These values are also in the table
 
For a ring final, use an end-to-end reading, eg. the line conductor r1.

Length of conductor = resistance of conductor ÷ resistance of conductor per meter

For a 2.5mm² conductor, resistance per meter is 7.41mΩ, or 0.00741Ω. So:

Length of conductor = r1 ÷ 0.00741
 

Reply to Eicr ring main readings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
Replies
26
Views
2K
Hi all Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block...
Replies
16
Views
890
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
511

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock