Discuss Electrak - no RCBOs in the UK Electrical Forum area at ElectriciansForums.net

IAmSparkytus!

-
Esteemed
Arms
Reaction score
315
We have a customer in a large office block with all power in the building fed from an Electrak plug in busbar system. Lots of desks, lots of computers.

Noticed none of the track is on an RCD/RCBO but they’re wanting some of the floor boxes relocated.

Would this fall under the remit of needing to upgrade from an MCB? Guessing not as we wouldn’t actually be connected or disconnecting anything other than the plug feeding each floor box if even required (might be enough length on them to reach new position).

Would recommend upgrading to RCBOs anyways but where do I stand on needing 30mA protection when there are so many computers plugged into each likely having a high level of leakage?
 
nightmare, was asked to investigate random tripping of office sockets in a large office as you describe.
turned out, someone had been in and done an EICR, later to "fix" the C3 about rcd protection for sockets (2nd floor office) they had changed all the breakers for rcbo's
cumulative leakage from pc's printers etc was the issue.

explained the problem and quoted to split the socket runs in half and feed from the middle of each run to 2 separate rcbo's
didnt hear a peep from them, i expect they gave the in house maintenance bloke a round of **** and told him to put it back how it was!!
 
We have a customer in a large office block with all power in the building fed from an Electrak plug in busbar system. Lots of desks, lots of computers.

Noticed none of the track is on an RCD/RCBO but they’re wanting some of the floor boxes relocated.

Would this fall under the remit of needing to upgrade from an MCB? Guessing not as we wouldn’t actually be connected or disconnecting anything other than the plug feeding each floor box if even required (might be enough length on them to reach new position).

Would recommend upgrading to RCBOs anyways but where do I stand on needing 30mA protection when there are so many computers plugged into each likely having a high level of leakage?
I have seen this loads of times, I work in an office environment, what we do is make sure the individual sockets on the desks have RCD protection at the socket and then nuisance tripping will not happen, of course the customer will need to pay for the sockets to be changed and if not you could just say the desks do not conform to modern regs but did confirm at time of fitting, this is a can of worms, a crown of thorns.
 
There used to be a guide of 3.5mA per workstation, so that allowed for 4 to keep under 1/2 I∆N, dunno is that accurate these days

Is this the SP 63A busbar trunking, there'd be a heap of equipment on that

Even if it didn't trip, you're still introducing a potential nuisance for when it does knock off the lot by front loading an RCD
 
There used to be a guide of 3.5mA per workstation, so that allowed for 4 to keep under 1/2 I∆N, dunno is that accurate these days
I recently measured a couple of items due to an odd RCBO tripping problem but found the modern desktop style PC PSU was only leaking about 0.5mA, the other stuff (monitor, network switch, both class II or at most FE) were more or less 0.1mA.
 

Reply to Electrak - no RCBOs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I am a removal man and I build office furniture. The company that I work for has based me at one of there clients buildings which...
Replies
10
Views
395
Customer has a set up using Electrak 63A under floor busbar, fed in 10mm armoured and backed up with a 63A c type mcb. From this he has 32A...
Replies
2
Views
1K
We have to put two new tower sockets in to a office at work. At the moment we have two towers but four sets of four desks. The two sets of four...
Replies
19
Views
2K
Hi guys, I've got a job where I'm installing dado trunking on the floor of an office for sockets and data. Some info on job - In total I will be...
Replies
18
Views
5K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock