Hi,

So my shutter door today started playing up.

Trips the RCD in house and garage but only when closing shutter. Does not have any problems opening.
So here is the head scratcher... once you reset the RCDs it closes fine..!!

Only thing I’ve done last week is paint the shutter, it’s driving me mad...

Any ideas greatly appreciated...
 
heavy rain got into the door electrics over last few days????? try a hair dryer.
 
Don’t think rain has got in as it as it’s a brick building and the shutter is protected.

The MCBs don’t trip just the CU’s RCD’s

Like I say I’ve only painted it which I assume is just a coincidence.

The fact that once you reset the RCD and then it works is baffling me.
 
Hi George - sorry to hear the door is playing up. Taking the "easy road" when extending power to a garage often results in 2 RCDs in series on the same circuit. This almost always means that both will trip if there's a fault, as they both see it.
Does the garage door opener plug in? Perhaps try it on an extension lead back into the house to eliminate the garage wiring from the mix.
 
Hi, I would guess it’s 20 year old, but that’s a guess as we have only lived here 6 months, to operate it there is a key switch on the left wall, I’ve checked that dry as a one and working perfectly.

8D96B1F5-8825-43F8-8061-CC4BED378E25.jpeg
 
Possibly leakage from one or other motor windings that are at different voltages from earth depending on direction, likewise limit switches if they work at mains voltage.

Tripping once and then operating without tripping is a bit peculiar but not unheard of. Sometimes it just takes a whiff of voltage to drive off a leakage path momentarily. Also, if a DP relay is slightly snappier to pull in the second time, it can avoid a capacitive leakage transient that sometimes causes a spurious trip if the line pole closes fractionally before the neutral.

There are various other possibilities but they are all a bit vague. Would need some proper test results to make headway troubleshooting this. If you find the fault, please let us know as it is an interesting one.
 

Reply to Electric large shutter tripping RCD in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi all, Curious one and hopefully some one of you could give me some advice. A customer has had a steeltech shed installed at their premises. A...
Replies
17
Views
1K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
643
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
346
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock