Discuss electric testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

W

werner starbuck

[h=1]Identify one item that needs to be disconnected prior to carrying out insulation resistance tests?[/h]here is another question that i'm not sure about. you can't disconnect the main earth as it is the resistance your testing, or ami wrong here.
 
Given the wording I assume this is a 2391/5 question. So you are doing a full L-N, L-CPC, N-CPC test?

You need to think about what would happen to equipment connected to the circuit. Both in terms of how it might affect the result and what 500V might do to equipment.
 
there are only four possible answers to the question.
1 sockets
2 switches
3 lamps
4 main earth

i have researched through all the study material and the only possible answer i can find is in the inspection and testing manual p74 411.3.11 onwards. it states that: 'insulation resistance tests should be made on electrically isolated circuits with any electronic equipment which might be damaged by applicationof the test voltage disconnected or only a measure to protective earth, with the line and neutral connected together.'

so based on this i think it should be lamps.
 
thanks for your help on this. i think i have it. if the sockets are disconnected and the switches on you would eb able to carry out the ir test without the risk of damaging any vunarable equipment.
 
not only plug in equipment , but as malc. has said, any lighting with electronics, ballasts etc., can be damaged. if in doubt, link L to N and test to E.
 
ok talking poo, i knew somone was talking/telling me poo when saying that other night... he must of been looking at selv or something... forgive my blunder
 

Reply to electric testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi. The question is..... can saturated ground affect earth resistivity testing equipment? Some days there's an unacceptable earth reading, another...
Replies
8
Views
358
Quick question. I am new to electrical installation so please be patient. You guys are great at answers. Re Insulation Testing. Why if I test...
Replies
12
Views
824
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
663
Hi All DALI lighting system distributes circuit via LCM's, for electrical test, do you stop at the LCM or light point. how do you carry out...
Replies
2
Views
393
Insulation test live to earth = 0.7 ohms. This is a long length of buried swa cable (approx 100m) from mains in to submain. Test done with live...
Replies
35
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock