Hello,

Can someone please help me describe what is going on in this wiring diagram I have drawn. I will upload the diagram and my poor description to go with it.

Thank you.

IMG_6466.jpg


IMG_6518.jpg
 
sounds right. the pme earth has not been carried into the evcp, which has been made into TT. however, it's a poor diagram as rhe pme earth should proect the cable to the evcp and be halted there.
 
The supply earthing you have drawn is TNS.
The description correctly describes TNCS.
The charging point is independently earthed of the main installation via a local earth electrode to provide a TT system.
The earth loop will use the ground to provide a return path back to the earthed star point of the transformer.
The supply earth is used to protect the supply cable from DB to charging point but then insulated from the charging point so that the two earthing systems cannot be simultaneously accessible.
The diagram could be changed to something like the below to match the description.
TNCS to TT IMG_6466.jpg
 
The supply earthing you have drawn is TNS.
The description correctly describes TNCS.
The charging point is independently earthed of the main installation via a local earth electrode to provide a TT system.
The earth loop will use the ground to provide a return path back to the earthed star point of the transformer.
The supply earth is used to protect the supply cable from DB to charging point but then insulated from the charging point so that the two earthing systems cannot be simultaneously accessible.
The diagram could be changed to something like the below to match the description.
View attachment 40482
...and link your neutral and earth terms in the SH and meter.
Christmas comes late, eh.
 

Reply to Electrical assignment help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone Just looking for some advice and guidance on approaching my HNC in electrical engineering and bridging units. How did other people...
Replies
3
Views
619
I have not had to do the wiring for a wet underfloor heating system before. I think I started a thread fairly recently and had some very good...
Replies
24
Views
2K
Hello, disclaimer: this is DIY and I am rather ignorant about electrical works. I just moved into a new rental apartment and i wanted to connect...
Replies
11
Views
518
Hello fellow electricians, Would anyone know how to connect a Nalder Bros & Thompson LTD London, please? ~The BS 89 is a tough book to obtain. I...
Replies
7
Views
845
Hi Guys Changing my heating/water programmer and im stuck on the wiring ive gone from a danfoss to a Drayton and the wiring description is...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock