Discuss Electrical test on D.O.L fed straight from main panel isolator in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
1
Hello everyone

i recently got a job on replacing a BMS panel in a plant room. the NEW panel i installed except the control side of the install also feeds the mains for a few gas boilers, immersion heaters and cylinders, pumps. etc. I am going to do the testing on that and i realised that some of the D.O.L circuits in the panel are is not fed from a MCB but are connected straight to the isolator that is fed from the main DB. meaning that the only for of protection on the D.O.L is the 50A mcb that feeds the panel.

now up to the D.O.L circuits the wirings is done with 10mm singles and on the outgoing side with lower rating cores depending the rating.

is that acceptable and if how do i record the DOL on my EICR?

i am New to testing as well so i don't have a lot of experience specially when it comes on BMS panels
 
Are you certain these circuits are connected directly, have you missed anything?
I've worked on hundreds of BMS panels and never seen any circuit without suitable protection.
 
Are you certain these circuits are connected directly, have you missed anything?
I've worked on hundreds of BMS panels and never seen any circuit without suitable protection.
Yes most positive. i physically traced the cables going to the main isolator, and i also have it on the drawings. thats the picture of it and basically is as shown on the drawingsScreenshot_20220928-215918_Word.jpg
 
Last edited by a moderator:
Assuming these DOL starters include overload protection then I dont see any technical issue.
The 10mm singles should have adequate fault protection from the 50A MCB and overload protection is provided by the overloads on the DOL.
 
Assuming these DOL starters include overload protection then I dont see any technical issue.
The 10mm singles should have adequate fault protection from the 50A MCB and overload protection is provided by the overloads on the DOL.
Yes they do have overload protection.
Electrically i don't see something wrong aswell but then how do i record this on the test sheet where i usually have the type of the mcb rating etc get max ZS permitted and everything.
 
So I did a bit of research online and I found that the motor starter that is used is in accordance with iec 60947-4-1 . I will have to calculate the max zs through the equation from the info thats provided in the starter datasheet.
 
Yes they do have overload protection.
Electrically i don't see something wrong aswell but then how do i record this on the test sheet where i usually have the type of the mcb rating etc get max ZS permitted and everything.

Find out the max Zs and record each one as a new circuit.

Or else create your own record of test results that is better suited to the type of installation.
 

Reply to Electrical test on D.O.L fed straight from main panel isolator in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Evening, I've been asked to install a supply to a sprinkler system in a new installation that must be separate to the building electrical...
Replies
2
Views
564
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
861
I have a main panel beside my meter on the house built in 1987. Then a 4 wire feed into a 200 amp panel on an inside wall of my basement. All of...
Replies
1
Views
390
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hello, I am a homeowner and have a solar project coming up. I intend to install a 9kw solar system but I am not sure if I have to upgrade my main...
Replies
2
Views
945

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock