Discuss Electrician advice please in the The Welcome Forum area at ElectriciansForums.net

duffy87

DIY
Reaction score
35
Hi all recently had smart meters fit, after the installation the technician couldn't get the sockets to turn on they just kept tripping. Turns out all the sockets in the house are on one RCD which I believe that's a problem in its self. But after 43 hours of no sockets in the house not working my land lord finally came with an electrician so he says, just found out he fits stair lifts and he admitted he only had his 16th edition. He's changed an RCD and removed wiring for a single plug socket in the dining room which he says was tripping the switch. My questions are should all my sockets in the house run into a single RCD and 2 is some one with a 16th edition even allowed to carry out these works?

Thanks
 
It's not a good idea having all your sockets on one RCD, but then the issue only started when you had the smart meter fitted. There have been a few cases where the RF emissions from the smart meter can cause some RCDs to trip. Is your meter close to your consumer unit?

And it's not a good sign if the electrician who visited has not kept up to date with regs.

I'd be very suspicious of his findings to be honest. Why change an RCD if he found a faulty socket circuit? Did he actually test anything?
 
Hi all recently had smart meters fit, after the installation the technician couldn't get the sockets to turn on they just kept tripping. Turns out all the sockets in the house are on one RCD which I believe that's a problem in its self. But after 43 hours of no sockets in the house not working my land lord finally came with an electrician so he says, just found out he fits stair lifts and he admitted he only had his 16th edition. He's changed an RCD and removed wiring for a single plug socket in the dining room which he says was tripping the switch. My questions are should all my sockets in the house run into a single RCD and 2 is some one with a 16th edition even allowed to carry out these works?

Thanks
I see a few issues here
The first being that the guy fitting the meter could not get the sockets to turn on following the installation of the meter
It is conceivable that the wiring to a socket could cause an RCD to trip but why was this only after a smart meter was fitted
In the past it was normal to wire a number of circuits to a single RCD but not that common now

If the wiring has faults it begs the question has the installation had an EICR done in the last 5 years and if it has who did the EICR on the property
 
It's not a good idea having all your sockets on one RCD, but then the issue only started when you had the smart meter fitted. There have been a few cases where the RF emissions from the smart meter can cause some RCDs to trip. Is your meter close to your consumer unit?

And it's not a good sign if the electrician who visited has not kept up to date with regs.

I'd be very suspicious of his findings to be honest. Why change an RCD if he found a faulty socket circuit? Did he actually test anything?
He never tested anything, he was surprised when he turned the mains off that the lights went out and he couldn't see lol. Sockets used to trip atleast twice a week before the meter was fitted. Was only after it was installed it gave up all together. He said he changed the RCD because it was proper burned is how he put it. He's removed the wiring from the socket and the sockets have stayed on for the time being.
 
He never tested anything, he was surprised when he turned the mains off that the lights went out and he couldn't see lol. Sockets used to trip atleast twice a week before the meter was fitted. Was only after it was installed it gave up all together. He said he changed the RCD because it was proper burned is how he put it. He's removed the wiring from the socket and the sockets have stayed on for the time being.

Yes, I'd a feeling that no testing was done. Has your landlord had an EICR carried out recently? It's a legal requirement.
 
I see a few issues here
The first being that the guy fitting the meter could not get the sockets to turn on following the installation of the meter
It is conceivable that the wiring to a socket could cause an RCD to trip but why was this only after a smart meter was fitted
In the past it was normal to wire a number of circuits to a single RCD but not that common now

If the wiring has faults it begs the question has the installation had an EICR done in the last 5 years and if it has who did the EICR on the property
I'll be honest I am a roofer I have no idea what a EICR is, he had some guy come and test the electrics not so long ago, my wife was home and heard him n the landlord talking in the cellar about the mains box, she couldn't hear exactly what was said but she 100% heard the landlord say just pass it and I will get it sorted. Nothing was ever sorted.
 
I'll be honest I am a roofer I have no idea what a EICR is, he had some guy come and test the electrics not so long ago, my wife was home and heard him n the landlord talking in the cellar about the mains box, she couldn't hear exactly what was said but she 100% heard the landlord say just pass it and I will get it sorted. Nothing was ever sorted.
An EICR is a report on the condition of the electrical installation.

I'd ask him for a copy of the EICR. Post it up on here, but with names and addresses redacted
 
An EICR is a report on the condition of the electrical installation.

I'd ask him for a copy of the EICR. Post it up on here, but with names and addresses redacted
I think we may have a copy I'll check later would u also like a picture of inside the box, seen as tho the smart meter lad decided to take it apart and start messing.
 
New posts

Reply to Electrician advice please in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all, Curious one and hopefully some one of you could give me some advice. A customer has had a steeltech shed installed at their premises. A...
Replies
17
Views
1K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
737
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock