Discuss Emergency Lighting Design in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

using a 2 pole keyswitch, take L through key to L on em. then take sw.l from normal light switch and feed through other pole on k/s to L1 on em. that way the k/s will cut both live feeds to em.and the normal switch will cut the switched L when the lights are turned off.
 
Ahh, i see how you can do it now.

To clarify, a permanent live (lets say straight from lighting circuit mcb) runs through one pole of the keyswitch to supply the fitting permanent live.
Then the live from the normal light functional switch passes through the keyswitch other pole to the sl on the EL. If i feed this live off to the normal lights before it passes through key switch i can remove all power to the EL's whilst keeping the normal lights on.

Correct?
 
And if you have a perm live and a neutral at your existing light switch it makes it even easier as you can just run a three core from there.
p/l s/l and neutral
 
Appreciatte the input guys.

Ive been doing plenty of research the last few days regarding the requirments and its a far more indepth subject than one would first think.

The workshops i am installing the E-lights in are lit by discharge fittings (SON/MH) spread across 3 phases ( i.e workshop A has 12 lights, 4 on L1, 4 on L2 and 4 on L3 with a 3 gang gridswitch). I take it im ok supplying all the EL's (for a particular workshop) from just one phase so id then have a 4 gang gridswitch (1 gang for the keyswitch module) with all the EL's say from L3?

Couldnt find anything in BS5266 regarding this today although it seems like the only way it should be done?

Regards
 
strictly speaking the em's should be tied to the individual light circuits.your way means that if the lights on L1 and L2 failed, the em's would not activate unless L3 circuit went down.
 
Appreciatte the input guys.

Ive been doing plenty of research the last few days regarding the requirments and its a far more indepth subject than one would first think.

The workshops i am installing the E-lights in are lit by discharge fittings (SON/MH) spread across 3 phases ( i.e workshop A has 12 lights, 4 on L1, 4 on L2 and 4 on L3 with a 3 gang gridswitch). I take it im ok supplying all the EL's (for a particular workshop) from just one phase so id then have a 4 gang gridswitch (1 gang for the keyswitch module) with all the EL's say from L3?

Couldnt find anything in BS5266 regarding this today although it seems like the only way it should be done?

Regards

If I am understanding you right then what you are suggesting would put a 415v potential in the light fittings if you are running your lights from L1 but have L3 for the Perm supply?
 
mmm, see the argument telectrix but even if L1 and L2 was lost the EM's would still be on (they are exit sign bulkheads above doorways which is why the client wants them on the whole time the place is 'open' - hence the desire they come on with normal lighting).

So if L1 and L2 are lost the EM's are still on and there would be adequate lighting from the 4 normal fittings of L3 to be able to aid escape aswell.
 
Is it ok to have 3 phases in that arrangement??? As you would have 3 different points of isolation in one accessorie.
Or does it just require a warning label above the switches.
 
Its permitted Dazza yeah.

You see it all the time in industrial setups - a 3 gang gridswitch with the 3 gangs each supplied with a different phase and feeding out to fittings from there.

Your correct in that a 400V warning label is required though.
 
I can imagine Tiny, ive seen a similar thing with a timed supply to Ambirad heaters........very dangerous and makes you wonder how some 'sparks' manage to sleep at night!
 

Reply to Emergency Lighting Design in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
649
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
626
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
843
Hi all can a Maintained emergency exit bulk head light fed from non lighting circuit if it is correctly fused and test point provided if no...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock