Discuss Emergency lighting help in the UK Electrical Forum area at ElectriciansForums.net

J

Jon West

Good afternoon,

yesterday we had a power cut in our care home, 2 emergency lights did not kick in. They kick in on the key flick test which i do every month but they do not kick in when i switch off the MCB in the consumer unit. We have just had new batteries put in and they are fully charged. The green led is on when the power is on. We do have a contract for maintenance with Lowe and Oliver but as maintenance manager if i can fix it it will save the call out fee. Any ideas why they would work on a flick test but not a full power cut?
 
try turning off the MCB again and see if the green mains LED is still on. this would indicate that they were fed from elsewhere.
We have 6 EL on the circuit i am turning off, all the led indicators go off and 4 EL kick in but 2 don't, all 6 work on the flick test.
 
Are they maintained fittings because you may have an issue will dual supplies from different circuits, if possible turn all the lighting breakers off.
 
How many lighting circuits does the op have?
in this consumer unit 20, but only 1 labelled corridor lights, which is the circuit i need. We have just had a full test and inspection so i know the CU is all labelled correctly and i can be 100 percent certain i am on the right mcb for the lights in question.
 
I might have got confused here, so they function with the test facility but not when you turn the breaker off.
 
I might have got confused here, so they function with the test facility but not when you turn the breaker off.
Correct, the lights work well daily, and the light kicks in on EL flick test, but not when the mcb is switched off or like yesterday in the event of a power cut.
 
I am just wondering if you are quickly flicking them on with the test facility to verify operation but when you turn off the breaker there is sufficient time getting to the fittings from the board for them to fail in other words they briefly illuminate and then fail.
 

Reply to Emergency lighting help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
640
I've been asked by a client to 'mask off' the green LED charging indictor lamps within several emergency lights fitted within bedrooms on a...
Replies
11
Views
661
Hi all Got a question regarding HMO compliance. Visited property today for landlord looking to apply for an HMO license for one of their...
Replies
5
Views
1K
Afternoon all... The customer has a number of small green lights in the ceiling that are always on. This is a bed and breakfast/hotel. I had...
Replies
6
Views
5K
Hi So I'd like a maintained emergency light but without the automatic emergency function to trigger in the event of power failure. In other words...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock