Sounds to me like several things may be being confused:

Fire exit door - a means to escape the building when there is a fire. Needs appropriate signage, lighting and door handles to help people exit in a hurry. I would have thought the rules don't care if the door is open or not when there is no fire.

Fire door - a door that needs to resist the spread of fire. Often between fire compartments in a building. These need to be closed when there is a fire to do their job. Various ways are used if making sure they are closed in a fire are used like signs saying "keep shut", springs that close the doors, automatic closing doors etc


It sounds to me like the problem may be that it is a fire door and that the way they are ensuring it is closed in a fire is by keeping it locked shut. Are there springs/door closers on the door so that it closes automatically when you do open it?
Nope, no springs on the door. Also it's a disabled access door.
 
What are peoples thoughts on keeping the main lighting on when doing an EM test. I always try to wire them so the main lighting stays on but you can still carry out the emergency lighting 3hr test. but I have a problem when they are combined fittings, you cant tell whether they are running on emergency or standard power.
 
What are peoples thoughts on keeping the main lighting on when doing an EM test. I always try to wire them so the main lighting stays on but you can still carry out the emergency lighting 3hr test. but I have a problem when they are combined fittings, you cant tell whether they are running on emergency or standard power.
Is the charge indication led not visible?
 
What are peoples thoughts on keeping the main lighting on when doing an EM test. I always try to wire them so the main lighting stays on but you can still carry out the emergency lighting 3hr test. but I have a problem when they are combined fittings, you cant tell whether they are running on emergency or standard power.
Agree the mains lights should stay on durring test mode except the combined ones of course. As suffolksparks says. The LED indicator will not be illuminated in test mode . And label the el fitting to avoid any confusion
 
What are peoples thoughts on keeping the main lighting on when doing an EM test. I always try to wire them so the main lighting stays on but you can still carry out the emergency lighting 3hr test.

You should always wire them this way as that is a requirement of the emergency lighting regulations.

but I have a problem when they are combined fittings, you cant tell whether they are running on emergency or standard power.

Switch the normal lighting off for a few seconds and you will see which are working in emergnecy mode.
 

Reply to Emergency lighting regs in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top