J

jamminuk

Hi,

Just a quick one, tested a ring today after new install, 2.5 singles in conduit. When i cam to do the end to end test i had these results:-

Flat ring

r1 = 0.44 rn = 0.44 r2 = 0.36

Kitchen ring

r1 = 0.23 rn = 0.23 r2 = 0.15

Not sure why the r2 was lower on both circuits if all are the same length and csa, are these reading acceptable?

Thanks

Ben
 
Archy - That did cross my mind, however the kitchen ring is in mini trunking (forgot to mention) and the flat ring in metal conduit. hmmmm

Murdoch - That did also cross my mind but cant think where these paths could be, especially in the kitchen ring, but i suppose somewhere along the line it must be

Thanks guys
 
Not really acceptable for an initial verification.
You should ensure that there are no parellel paths and re-test.
This is one of the reasons why some tests should be conducted during construction rather than after construction is completed.
 

Reply to End to end test r2 greater then r1 & rn in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top