Discuss Unusual Ring Final Tests in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Reaction score
29
After fixing a few CPC related issues on a ring final I got the following results

L-L = 0.47
N-N = 0.47
CPC-CPC = 0.69

R1+R2 Tested at 0.31
R1+Rn Tested at 0.25

All looks good, until that is I realised that the CPC-CPC is actually not quite right. It should be 0.78 (0.47 x 1.67 for a 2.5/1.5 T&E). But if that was plugged in (so to speak) the R1+R2 values are then wrong, but they are correct, so the readings at the board for the CPC are in fact right.

My assumption is that the cable used in the building is of a rather cheap variety and the conductors are actually 2.5/1.7. If you use that then the calculations match the readings.

I suppose you could argue the CPC readings are just outside tollerance (0.05 is the usual max, and this is 0.09), but I've not seen this before with my tester.

Anyone got any thoughts, or have you seen this type of thing yourselves. Is my assumption feasable that the conductors might not be exactly 2.5/1.5 ?
 

Reply to Unusual Ring Final Tests in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K
Did a check on a ring circuit, due to board having to remain live I did it at a socket.. Was an RCBO, had checked RCD side and all tested ok...
Replies
3
Views
1K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
996

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock