Discuss Energy Consumption on 3-phase with solar into one phase in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

P

PvNewbie

Hi

Quick question about a system a user wants who has 3-phase electricity. If we install a 4kWp system onto one phase, when it is generating more power than is being used by that phase, will the other phases consume that power, thus slowing/stopping the meter, or is it lost back to the grid?

Cheers

Newb
 
Agree that the power will go back to the grid but there is possibly a difference on what the meter will read depending on what type it is and how it aggregates the power consumption across the phases. It is conceivable that an old spinning wheel 3 phase meter will be better for a consumer than a modern digital one. For example say:
L1= 100W (import) L2 = 100W (import) L3 = -100W (export)
An old analogue meter might read 100W (import)
A new digital meter might read 200W (import)
You may find it difficult to get definitive info though.
 
We had 4kw on one phase, the meter never showed R.E.D, we then fitted an additional 2 x systems at a later date, we now find on an average day we only use 4 units of electricity overnight, the rest of the time the meter is showing R.E.D, currently we are producing about 45Kw a day from 10Kwp of Panels.
 

Reply to Energy Consumption on 3-phase with solar into one phase in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
964
Help please, this is my first post on this subject regarding solar panel / battery installation into house with 3 phase supply. I am a DIY level...
Replies
0
Views
1K
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
For power outages, my solar inverter (+battery) is able to take on the entire house load - as long as I unplug my collection of vintage kettles...
Replies
3
Views
919
Greetings, everyone, After dedicating over a month to researching Solar PV systems, I'm nearly ready to make a decision. I owe my progress to...
Replies
1
Views
932

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock