Discuss Energy Suppliers request Cert in the UK Electrical Forum area at ElectriciansForums.net

H

highspark

I am attending a job tomorrow in which a landlord needs to have the supply turned back on by the Energy supplier. They have requested a certificate from an electrician to ensure (customers words) the installation is safe.

i am I right in thinking a condition report is what they are after. Obviously only dead tests can be completed...
 
The last one I dealt with the supply had been disconnected as the install was unsafe,as you say all you can do is dead tests and note on sheet that no live tests were done due to lack of power.
 
They will want an EICR or EIC (depending on what has been done on your part) so they can be sure under their duty of care in the knowledge that the installation is safe before they re-instate the supply to it.
 
Last edited by a moderator:
I called them in cos a new fuse board had been fitted . For me a 2 hour journey one way ,so I arrived
He said got your very
Me no I faxed it over when I had you come over and if you had not received it you would not be here
Him no I need to see it
Me but the person who sent you here must have the copy I faxed over
Anyway to make it short he left
So rang them yes we will come back 2 or 3 days later.
So next chap turns up
Me here is the paper work
Him I can't change it as you have a new fuse board and I am a grade 2 meter fitter and I only change meters in original settings where nothing new has been done
Me I think your telling me find and I am going to ring your office and you can't leave this flat till I speak to some one (that's putting it politely)
He was right it seems . There is a grade 1 and a grade 2
So he went
I rang again an hour later and was told he had to have a week of work for the stress I had caused him .They would only send out 2 fitters and just to teach me a lesson they would turn up about 8pm.
I asked to speak to her boss to complain about what she said as all calls are recorded but that day they weren't working
Hope you understood all that
 
They will want an EICR or EIC (depending on what has been done on your part) so they can be sure under their duty of care in the knowledge that the installation is safe before they re-instate the supply to it.

Never been to the property before. So presuming it's the way it was in 2008. I'll just give him the cert, pass or fail it's up to him.
 
Never been to the property before. So presuming it's the way it was in 2008. I'll just give him the cert, pass or fail it's up to him.

Eh? You need to carry out a full EICR up to the point of live testing and then carry out the live testing once the supply is available.

You won't know what condition it's in until you inspect and test it.
You will likely find some low IR as, assuming there has been no heating, damp will have crept in everywhere.
 
Why?, with the provision of self connect meters.

You can't assume they will change the meter to a self connect type.
We don't know what has been done to make the supply dead, they might have disconnected the consumers tails and removed the fuse or maybe they dug up the road/climbed the pole and chopped the supply.

And he would still have to go back if it's a self connect meter to make the connection.
 
If it was killed in 2008 the chances are it was/is a 16th edition installation.
Do you not think that it should be treated as a new installation and brought up to current standard prior to energising?
 

Reply to Energy Suppliers request Cert in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K
We have had builders in, who have stopped for Xmas. My daughter tried to do a wash. The wash machine wouldnt. Its power socket is dead. I...
Replies
4
Views
691
What are peoples opinion's on this, pair of big old semi-detached houses (85 and 87) converted into apartments, dont think its a HMO although it...
Replies
1
Views
276
Hi, So I'm trying to understand what's going on with my off-peak electricity supply, as something's wrong with it and I'm trying to determine if...
Replies
5
Views
1K
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock