Discuss Everything RCD protected? in the UK Electrical Forum area at ElectriciansForums.net

N

Noob2013

Hi all,

My understanding is that everything should be RCD protected now, as it is unlikely that all the criteria is met for it to not need RCD protection.

I went to my friends house the other day and the consumer unit had a periodic inspection and test carried out by the local council last week.

I noticed that the cooker, lights and smoke alarm circuit is not protected by RCD, but the shower and sockets are.

Should the other circuits be RCD protected?

Thanks
 
What did the report say exactly, did it express the installation doesn't meet current regulations but was wired to the reg' at date of installation....?
 
We are getting to the stage in a dwelling where it will be the Regulations that everything regardless of how it is installed and what it is will be covered by RCD protection.

The latest revision of 411.3.3 now states "Other than a dwelling" and I can see future revisions start to increase the scope until everything is RCD protected in a house.

But at the moment we are not there, and there are still things in a house that do not need RCD protection, especially if it was installed to a former edition
 
The regulations are not retrospective.
Current regulations for domestic situations in general require 30mA RCD protection for cables buried in walls (in certain circumstances), sockets rated <=20A, circuits in a room containing a bath or shower, outdoor use mobile equipment <=32A.
This does tend to cover most domestic arrangements but it is by no means universal yet.

There are other requirements for 30mA RCD protection for less likely scenarios in domestic and for some special locations, there are requirements for other RCD protection for different risks than additional protection or persons and livestock.
 
Ok thanks.

There was no report.

I'm going there to extend cooker circuit and therefore concerned that I should be making sure everything is RCD protected as I will be the last person touching that circuit.

I could make it easy and make the whole consumer unit protected by the one RCD.

What's everyone's opinion on whether I should leave it as it is or provide rcd protection?

Thanks
 
Well it is a matter of how your extend it really. If you are burying the cable you are installing in the wall then yes that piece of cable needs to be RCD protected unless you conform to regulation 522.6.204. If you are running it surface then you don't need to fit an RCD.

It does seem to be stupid that the existing cable of X length that is buried in the wall does not require you to put RCD protection on it, but if you bury Y length of your work, then that Y length needs to be protected!!!!

Depending on the client and whether he believes all this, I would recommend you protect the whole circuit with an RCD. But then a 25 pound small job of extending an existing circuit becomes a 150 pound major job of changing protection devices etc etc.

Don't make much sense to me. But they are the regs.
 
Ok thanks.

I could make it easy and make the whole consumer unit protected by the one RCD.
This option then means a single fault takes out the whole power supply and is not recommended.

I agree with malcolmsandford, correct and does not make a lot of sense but it is your new work that must be compliant with the current regulations (and the earthing and bonding if required for your work)
 
This option then means a single fault takes out the whole power supply and is not recommended.

I agree with malcolmsandford, correct and does not make a lot of sense but it is your new work that must be compliant with the current regulations (and the earthing and bonding if required for your work)
Agreed but my work is the lighting and cooker so either an rcbo for each or all on rcd
 
As they said ^^^ Don't put everything on one RCD !!! Daz
 

Reply to Everything RCD protected? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
770
My friend just moved into a new build flat and its for a disabled person with a hydraulic lift to go to the upper floor. There was/is a leak...
Replies
8
Views
447
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
808
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Evening all, If a socket circuit is not RCD protected via an RCD/RCBO and there isn't the option of fitting an additional RCD enclosure or...
Replies
20
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock