Discuss Exhibition Trailer Generator in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
643
Testing 2 exhibtion trailers with the same setup. Power is provided by a generator with a main switch which runs to a consumer unit about 1 metre away. The consumer unit main switch is an RCD, the CU then houses 5 MCB's. Now theres no OPD placed between the generator and the consumer unit but is this a problem?.

4 16A MCB's and 1 10A MCB the generator is easily capable of this load. The consumer unit is fed with 25mm tails. Now BS7671 says overload protection may be placed along the run of a cable within 3 metres which it is. But the only overload protection provided are the MCB's.

Do you see a problem here? What code?. The whole installation is abit of a funny setup, Ive been scratching my head quite a few times with different problems thinking is this acceptable, and just left with this one.

Thanks.
 

Reply to Exhibition Trailer Generator in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
558
Hey guys and gals. We bought a small office trailer that is wired up. It's never seen mains power and uses a generator disconnect (220). I read...
Replies
0
Views
1K
I had a PV system installed by a local reputable manufacturer last autumn; since then, I've received conflicting advice regarding the consumer...
Replies
2
Views
2K
I am not an electrician, but have one that is not very familiar wit generators. The planer is a 5 hp 20” grizzly planer with magnetic switch and...
Replies
1
Views
828
Hello everyone, I'm currently working on a project to upgrade an existing renewable energy system and could really use some expert advice. The...
Replies
0
Views
675

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock