Discuss extension leads with surge adaptors in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

multimick

-
Esteemed
Arms
Reaction score
289
don't do much pa testing but noticed a couple of times these show reverse polarity on my megger pat 120 ,but test the pins for continuity and its ok on neutral and earth but no continuity on line,they all work ok ,is the electronics causing problems ?
 
There's a good case to test at both 500V to prove the functionality of the SPD and 250V to obtain a 'normal' value for typical conditions, i.e. without the SPD operating.

If the 500V test returns a high resistance value, then the SPD is not going to be of any use in a real over voltage situation during operation.
 
There's a good case to test at both 500V to prove the functionality of the SPD and 250V to obtain a 'normal' value for typical conditions, i.e. without the SPD operating.

If the 500V test returns a high resistance value, then the SPD is not going to be of any use in a real over voltage situation during operation.
My understanding of how SPDs work, is that every time there is a surge, material is lost.
Eventually, if there are enough surges, the device has to be replaced.
Testing at 500V will reduce the life of the device.
 

Reply to extension leads with surge adaptors in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
709
Hi All, My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our...
Replies
8
Views
512
Hi Hope anyone can help Can someone give me advice on how to connect up a 3 phase to 13amp adaptor lead for carrying out PAT testing on 3...
Replies
17
Views
3K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
757

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock