Reaction score
2,392
Can anyone recommend light sensors (independent) for a large car park. Must have lux and movement control. To switch around 20 lights on at a time. Load might typically be in the order of <750w. the car park is roughly 80m long and 50m wide, very roughly. There are a few corners Kind of like a lower case d shape with the narrow end about 20m but straight as opposed to irregular. We have about 20 lights outside units on one side. Several lights on other units LED floods, and finally 25 LED bulkheads (currently switched by lux controller) Client wants to save energy so asking for quote for sensors to switch on lights at night. They need to be top quality though. The picture is the main building to the right is another single storey and to the left is another two storey each unit with a light outside basically.
 

Attachments

  • 279.JPG
    668 KB · Views: 14
Last edited:
Agree with DefyG. Steinels I have fitted had a range of 20m in all directions when fitted 2m from ground level. They are the best ones I have worked with.

Not sure of the max switching load. It's been a while since I fitted one.
You might have to use it for a relay control.
 
Incandescent / halogen lamp load 2000 W
Fluorescent-lamp electronic ballasts 1500 W
Fluorescent lamps, uncorrected 1000 VA
Fluorescent lamps, series-corrected 700 VA
Fluorescent lamps, parallel-corrected 1000 VA
Low-voltage halogen lamps 1000 VA
LED < 2 W 100 W
2 W < LED < 8 W 300 W
LED > 8 W 600 W
Capacitive load 176 ÎĽF
Looking at Steinel the above states loads it can take. I dont quite get what they are saying the load is on LED is can anyone interpret it, or throw some light on what it is saying only re LED?
 
Most of the large lighting ccts i have done, i have switched the lights using contactors rather then the sensor. In an extreme case, i wired the sensors back to a control centre and switched the lights using contactors, that way you could enable both dusk til dawn and manual over-ride, easily. You can of course just use a sensor per light.
 

Reply to External lux and movement sensors for external car park in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The garage is 17 mtrs x 15 mtrs in the UKh The house has a 100 amp supply to the house consumer unit. The garage consumer unit is fed from a...
Replies
4
Views
1K
Morning Gentlemen Question we are replacing a consumer unit for a landlord and he's been advised by another company to fit EI164RC smoke alarms...
Replies
11
Views
2K
S
Hi, I'm looking to install 4 outside lights across the front of our house, and i would really like them to be very "green". So i came across...
Replies
8
Views
7K
S
I have a request from a customer who basically wants a number of LED floods installed. However he wants it set up that all the lights come on when...
Replies
4
Views
2K
G
Hi all. Customer has asked if I can mount light fitting on top of an existing pole to illuminate a section of a car park. There is power local...
Replies
4
Views
648
goldie
G

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock