I have an external RCD unit to protect outside lights. This trips intermittently, when it does it also trips the RCD in the consumer unit. If I test the external RCD with the trip switch, it trips and also causes the RCD in the consumer unit to trip. I have tested the circuit and the tests are ok. Any ideas why the consumer unit RCD trips as well, both are 30mA.
 
I have an external RCD unit to protect outside lights. This trips intermittently, when it does it also trips the RCD in the consumer unit. If I test the external RCD with the trip switch, it trips and also causes the RCD in the consumer unit to trip. I have tested the circuit and the tests are ok. Any ideas why the consumer unit RCD trips as well, both are 30mA.
Because there is no discrimination/selectivity. The upfront RCD should be time delayed/S type if the installation method permits.
 
I have an external RCD unit to protect outside lights. This trips intermittently, when it does it also trips the RCD in the consumer unit. If I test the external RCD with the trip switch, it trips and also causes the RCD in the consumer unit to trip. I have tested the circuit and the tests are ok. Any ideas why the consumer unit RCD trips as well, both are 30mA.
Are you an Electrician?
 
Sort the problem that's causing the trip in the first place then the lack of discrimination won't be such an issue -
Hands up for outside floodlight
Hands up for pond feed
I need to drink less coffee!
 

Reply to External RCD trips Consumer unit RCD in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
Hi, I have a job for a customer, the consumer unit is an old 3036 board and there are several holes in it giving access to live parts, I can...
Replies
6
Views
702
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
661
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock